Sunny Island will run frequency all the way up to 65 Hz if necessary to curtail output.
Rule 21 or SA seem clear regarding ride-through indefinitely at full power, and stay on-line (I think at full power) for 299 seconds mandatory, disconnect by 300 seconds mandatory.
Near Nominal is now 58.5 to 60.5 Hz. I was able to fix my problem by setting low frequency of Sunny Boy to 58.9 Hz instead of 59.3 Hz.
Mechanical clock in an electronic stove? Or is that an electronic clock that uses line frequency for timing? Could be a poorly trimmed crystal based clock. ... and transfer one array with about half the solar back to the grid, in response to the battery voltage and the SI frequency...
diysolarforum.com
What I haven't seen clearly defined is frequency-watts.
Could be your inverter ramps down to zero watts right at 60.5 Hz, and it implements that mandatory cutoff above 60.5 Hz after 300 seconds.
I think, if frequency-watts has ramped down to zero output, it shouldn't be required to disconnect ever, for the moderately off-nominal frequency; just wait for frequency to come back within near-nominal.
I suggest reducing the frequency where your inverter reaches zero output, so there is some margin between that and 60.5 Hz, to allow for error/disagreement, also response time.
Here's something I just found, haven't studied: