I got a Champion 8kW back up generator dedicated for on-site power system.
A few details first:
My solar is located in my work shops next door to my home,
The solar is 7kW PV, twin MPP 6048 Inverters (each produces 120/240, each have internal N-G bond only during inverting mode)
Energy storage system is 760Ahr 48v LiFePO4 rack batteries some commercial units and some DIY.
For poor solar Nov-Dec period, I have a dedicated 30A 240vAC supply from the house to supply power for battery recharging off peak TOU,
For powering during on-Peak and during good solar (March - October) the solar supplies a Critical loads panel at the house, 30A 240vAC.
I liver rural in a place with lots of snow, high winter winds and big trees = we can have power outages that last 4 days.
The plan:
In the normal case, if solar is poor, the inverters will trigger charging with the 30A 240 grid supply. To prevent this from taking place during on-peak TOU, I have this power supply running through a 240vAC HWT Timer (Intermatic 30A 240v programable timer) this timer limits utility power from being available to the off-peak hours (7PM to 7AM Mon-Fri, all day SAT SUN). I have the Charge Trigger set high enough that even if the Inverters are 'looking for charging current' early in the morning, the large battery storage will run the full shop all day anyway, and at 7PM when the timer switches on utilty, then (and only then) the inverters go into by-pass mode, and charge the batteries. This has the side benefit of allowing any PV charging available to have already taken place.
My system Never supplies power to the utility.
So what about when the Grid is Down:
I have purchased the generator, a three pole Manual Transfer Switch, and an exterior Generator Plug 30A 240 4-pole.
I read the Generator manual, located and removed the N-G bond wire jumper, and put a label on the generator "Floating Neutral". A test with an ohm meter before removal of the jumper showed N-tied to-G in the generator, and after removal of the jumper, the ohm meter confirms Open between N and G. (the same if running or not).
The plan, is to install the MTS after the timer, to control N, L1, L2 Utility and N, L1,L2 Generator supply to the twin MPP 6048's. The existing Ground bare wire from the utility will pass through the MTS and tie to the generator G. I believe this is key, along with the removal of the N-G in the generator.
My thoughts are, if utility is unavailable and batteries are getting low, I can start up the 8k generator, warm it up, plug it into the exterior wall plug, then turn the MTS from Utilty to Generator and let it run long enough to recharge the battery packs. At 7:00 PM the shops are not running equipment, so loads are low power items mostly lights. The MPP's will use by-pass for any loads while charging up batteries, in by-pass the MPP's break their internal N-G bond, and rely upon the 'grid'. With the Ground from the transfer switch passing through and connecting to the generator wall plug, I believe I maintain a single point of N-G bond (back at the utiltiy panel) and all should be well.
However since this is a complex issue, and asking for comments is less hazardous then blindly connecting 30A 240 (7kW) of power 'to see what happens' I thought perhaps someone would comment on the logic, I am in no hurry, grid is on tonight nothing is connected up yet (MTS and Generator are sitting patiently waiting on the shop floor).
A few details first:
My solar is located in my work shops next door to my home,
The solar is 7kW PV, twin MPP 6048 Inverters (each produces 120/240, each have internal N-G bond only during inverting mode)
Energy storage system is 760Ahr 48v LiFePO4 rack batteries some commercial units and some DIY.
For poor solar Nov-Dec period, I have a dedicated 30A 240vAC supply from the house to supply power for battery recharging off peak TOU,
For powering during on-Peak and during good solar (March - October) the solar supplies a Critical loads panel at the house, 30A 240vAC.
I liver rural in a place with lots of snow, high winter winds and big trees = we can have power outages that last 4 days.
The plan:
In the normal case, if solar is poor, the inverters will trigger charging with the 30A 240 grid supply. To prevent this from taking place during on-peak TOU, I have this power supply running through a 240vAC HWT Timer (Intermatic 30A 240v programable timer) this timer limits utility power from being available to the off-peak hours (7PM to 7AM Mon-Fri, all day SAT SUN). I have the Charge Trigger set high enough that even if the Inverters are 'looking for charging current' early in the morning, the large battery storage will run the full shop all day anyway, and at 7PM when the timer switches on utilty, then (and only then) the inverters go into by-pass mode, and charge the batteries. This has the side benefit of allowing any PV charging available to have already taken place.
My system Never supplies power to the utility.
So what about when the Grid is Down:
I have purchased the generator, a three pole Manual Transfer Switch, and an exterior Generator Plug 30A 240 4-pole.
I read the Generator manual, located and removed the N-G bond wire jumper, and put a label on the generator "Floating Neutral". A test with an ohm meter before removal of the jumper showed N-tied to-G in the generator, and after removal of the jumper, the ohm meter confirms Open between N and G. (the same if running or not).
The plan, is to install the MTS after the timer, to control N, L1, L2 Utility and N, L1,L2 Generator supply to the twin MPP 6048's. The existing Ground bare wire from the utility will pass through the MTS and tie to the generator G. I believe this is key, along with the removal of the N-G in the generator.
My thoughts are, if utility is unavailable and batteries are getting low, I can start up the 8k generator, warm it up, plug it into the exterior wall plug, then turn the MTS from Utilty to Generator and let it run long enough to recharge the battery packs. At 7:00 PM the shops are not running equipment, so loads are low power items mostly lights. The MPP's will use by-pass for any loads while charging up batteries, in by-pass the MPP's break their internal N-G bond, and rely upon the 'grid'. With the Ground from the transfer switch passing through and connecting to the generator wall plug, I believe I maintain a single point of N-G bond (back at the utiltiy panel) and all should be well.
However since this is a complex issue, and asking for comments is less hazardous then blindly connecting 30A 240 (7kW) of power 'to see what happens' I thought perhaps someone would comment on the logic, I am in no hurry, grid is on tonight nothing is connected up yet (MTS and Generator are sitting patiently waiting on the shop floor).