My husband and I are fairly new to solar - we have had our system for about 18 months. We purchased everything through an off-grid company in Canada but have had consistent issues and in doing our own research realized the components they sold us don't work properly together. We have already purchased a replacement inverter and generator and have recently been told we need new controllers as well. We have lead acid batteries that we want to switch out with Lithium, so we’re basically redoing everything. I have been looking at EG4 products and would love advice on the best way to go so that we get a system that works well without having to continually buy more components. Thank you in advance for your feedback.
Solar Panels we have: 16 panels 450 watts each (7200 W total) - specs are attached. We are going to re-wire into two strings of 8 panels each.
Batteries: Looking to buy six 48v 100AH EG4-LifePower4 battery kit (30 kWh) -
https://signaturesolar.com/eg4-life...enclosed-rack-with-door-wheels-busbar-covers/ OR six EG4 LL-S batteries
Current inverter: AIMS 12KW 120/240 split phase -
https://www.aimscorp.net/product/12...split-phase-output-etl-listed-to-ul-1741-csa/
Options for the remaining components to purchase:
Option 1. Keep current inverter and get 2 EG4 charge controllers -
https://signaturesolar.com/eg4-solar-charge-controller-mppt-500voc-100a-mppt100-48hv/ - each connected to a string of 8 panels
Option 2. Replace inverter and controllers with
two EG4 6000XP Inverters (
https://signaturesolar.com/eg4-6000xp-off-grid-inverter-split-phase/)
Options 3. Replace inverter and controllers with one EG4 12KPV inverter
https://signaturesolar.com/eg4-12kp...in-one-hybrid-solar-inverter/?_hsmi=315974474
Questions that come to mind are:
1. Any feedback from others who have experience with EG4 products? I have seen some good and bad reviews regarding tech support.
2. Any significant difference between EG4-LifePower4 batteries vs EG4 LL-S batteries?
3. EG4 inverters/controllers say a combiner box is not required - is that true?
4. Option 1 would be the least cost and allow us to keep a newer inverter we have already paid for, but not sure how compatible EG4 products are with it or if better to get all same brand? Also, our current AIMS inverter idle consumption is 200 kWh which is a lot compared to EG4’s (50 kWh) and it doesn’t allow manual settings (you select type of battery and that’s it). Positives are they have good tech support and inverter seems to be working well.
5. We are in Canada and have to charge batteries with a generator almost daily in winter. We have a 14 KW generator. With option 1 the inverters max charge current is 125Amps (6000W). If we charge when the batteries get to about 20% then if my math is correct it would take 4 hrs to charge the batteries to full (24 kW / 6000 kWh charge = 4 hrs)? If we went with option 2 or 3 we can charge faster (8000kWh with EG4 12KPV or 2X Faster with two EG4 6000XP inverters - 12000kWh). That is appealing as it would save running the propane generator extra time.
6. I want to make sure the wiring we have buried in the ground will work with any of the above options as our system currently trips breakers. Our solar panels and backup generator are approx 75 to 100 feet from the house where the batteries and controllers/inverter are. The electrician used #6 wire from panels to controllers, and #4 wire to connect inverter to generator. If we put 8 panels in a string, according to the specs it will be 11.6 amps and 394.4 volts to each MPPT so I understand that should work with both the EG4 controllers or inverters, and should also be no problem with the 6 AWG wire - is that correct?
Also, I am not sure about the #4 wire connecting the inverter to generator. Is this equation correct? Generator sends 14KW to inverter (6000 Watts for battery charge and rest for domestic use) / 240 volts = 58.3 amps in which case #4 wire should be okay?
Then for wire from inverter to batteries: 6000 Watts / 48 volts = 125 amps. If upgrade inverter to two 6000 XP’s it would double to 250 amps? What wire size can handle that?
Currently when we start the generator manually it runs no problem and the inverter shuts it down when the batteries are charged, but when we set the generator to automatically come on when the batteries get low it will stay on for 10 to 20 minutes then quit, and keep starting and stopping, so we’re not sure if that’s an inverter issue, or #4 wire isn’t big enough to handle the amps (though seems implausible if it runs fine manually), or a loose connection with the auto start.
I’m not sure I am thinking of all the angles and options so am open to any advice and suggestions. I know this is a lot of info but I want to make sure to get components that will work together well and last a while this time.
Thank you kindly