How you have it shown would connect it to the house ground when plugged in to the house power. When it isn't plugged in, your ground is floating, so you would want to tie it to a ground somehow (clamp to a grounded rod, or to a house ground, or something).
So if I ran a ground wire from the load panel ground straight back to the subpanel new ground busbar, that would cure the floating ground? Thanks again for your insights and patience with us wannabe electricians.
 
If subpanels are supposed to have no N and G bond, why are they allowed to sell them with a single busbar.?
 
So if I ran a ground wire from the load panel ground straight back to the subpanel new ground busbar, that would cure the floating ground? Thanks again for your insights and patience with us wannabe electricians.

Correct.

If subpanels are supposed to have no N and G bond, why are they allowed to sell them with a single busbar.?

1) Because some panels sold can be either a sub panel or main panel
2) Panels don't come with everything required (they don't include all breakers for example)
3) Because they can make an extra $6 off you for the separate ground bar!

Side note - the panel I bought to use as my critical loads sub panel was actually intended for a main panel, yet it came with its own separate ground bus bar. I didn't know it would, so I had bought an extra ground bar and now I don't need it. Go figure lol.
 
If subpanels are supposed to have no N and G bond, why are they allowed to sell them with a single busbar.?
Sub panels are also used as a small main service panels as well. Extremely small sun panels you connect the grounds without using the buss bar at all (or add one for convenience)
 
I don't know about your inverter, but EG4 manual calls for a #6 line off a 60 amp breaker.
Yes a AIO connected with a cord is a problem unless you scale back your charging rate and limit your consumption of power to the difference between the available incoming wattage minus the wattage used for charging
 
Ok, I got an answer from CHINS and they said that the N & G are NOT bonded together inside the unit. So based on my drawing I should place a connection between the N and G in the AC OUT breaker box? Yes or No? Also I added the gnd rod for the solar array. Is that okay?

Also, does anyone have a comment on the pic in post #20? Would that work or be a bad idea? Thanks
 

Attachments

  • 100W AIO 3S4P V2.png
    100W AIO 3S4P V2.png
    55.7 KB · Views: 5
Last edited:
Why again are you putting an AC plug on your inverter AC input? Why would you disconnect it? That seems to be a complicating factor for your N-G bond. If that stays connected, you shouldn't have to mess with any other N-G bonding anywhere. But if you disconnect the AC-IN to your inverter (including neutral) then yeah you'll do a N-G bond. But ONLY when that is disconnected.

If you insist on having that plug on your AC-IN, perhaps wire another "N-G Bond plug" that you then plug that into that will create your N-G bond when you are disconnected from the rest of the house. I.E. You unplug from the house input, and plug that into a single "outlet" that has a wire from N to G (and no H connection). That way, you can never have a second N-G bond by accident when it is plugged in to mains power.
 
This surprises me. Where is your AC In coming from?
Normal house outlet.
If I understand this exchange properly you at least at times attach your AIO to a house outlet if you bond after the AIO you will end up with to bonded neutrals not good. If you really want/néed to be bonded when off grid you will need to come up with a way to disconnect the of grid bond when you are connected to grid. Is this a camper solar system a solar generator or a system in a building?
 
Why again are you putting an AC plug on your inverter AC input?
How else would I connect to the house power?
Why would you disconnect it?
I don't plan on disconnecting it. I would like to have that to help charge batteries on those not so sunny days.

I added a disconnect switch, I had an extra battery one, and OFF would be open, and ON would connect N & G when the AC Input is unplugged. The added circuit is in blue. Would this work?
 

Attachments

  • 100W AIO 3S4P V2.png
    100W AIO 3S4P V2.png
    55.6 KB · Views: 4
Is this a camper solar system a solar generator or a system in a building?
It is a basement setup for now for brownouts if we have them. Eventually going into an RV which will have a lot of changes to put it in one of those. Another day and time.
 
How else would I connect to the house power?

I don't plan on disconnecting it. I would like to have that to help charge batteries on those not so sunny days.

I added a disconnect switch, I had an extra battery one, and OFF would be open, and ON would connect N & G when the AC Input is unplugged. The added circuit is in blue. Would this work?
If you are always connected to the plug you should be bonded through it when the inverter is on and connected to the plug you must not bond again after the inverter
 
How else would I connect to the house power?
You technically should have it wired separately into the circuit panel using the wire size and breaker recommended by the manual. You stood have a cutoff switch close to the AIO in case it must be shutdown in a hurry and to make it convenient and obvious when grid is disconnected from the AIO.
 
You are running into the same problem I had with my MPP 1012LV-MS. The AC In provides the N-G bond while plugged in ONLY when in AC pass-through. When Inverting, you have NO N-G Bond. I was instructed by Ian at Watts247 to tie the two neutrals together inside the AIO (I used a small jumper wire). This took care of the problem (as long as I never unplug the AC-In). This is why it is recommended to hard-wire it to a dedicated breaker in your panel.
 
You technically should have it wired separately into the circuit panel using the wire size and breaker recommended by the manual.
So in my drawing I do have the AC IN going through a breaker, with surge protect, going to the AIO. But you are saying not through a plug? Yes?
have a cutoff switch close to the AIO in case it must be shutdown in a hurry and to make it convenient and obvious when grid is disconnected from the AIO
So get the AC from a subpanel, through a breaker, then from there to the AC Input breaker box and surge protector?
 
Yes. Use appropriate size wire and breaker.

Tie the neutrals all together (Incoming neutral to the neutral bus bar in your loads panel, neutral output from inverter to the same bus bar).

Tie all the grounds together (incoming ground to the ground bus bar in your loads panel, ground connection from inverter to the same bus bar).

This will resolve all N-G bonding concerns and prevent floating neutrals.

I like how my Outback is wired - it has a spot for incoming and outgoing neutral, even though in the documentation it mentions there really isn't an "in" and "out" neutral as they are all tied together. But they did it that way to make it logical and easy to understand at a glance.
 
This is why it is recommended to hard-wire it to a dedicated breaker in your panel.
Now I see what everyone is saying. It is all about the plug. I have an unfinished basement and it has one outlet available. That is my dilemma. That is the reason for the plug. There is a subpanel in the basement but it was for a long retired hot tub. The breaker for it outside is shut off. So I am trying to come up with a way to make this as easy as possible but yet safe.
 
What size breaker and wire feeds that unused sub panel? Maybe repurpose that for the input to your inverter.
 
Now I see what everyone is saying. It is all about the plug. I have an unfinished basement and it has one outlet available. That is my dilemma. That is the reason for the plug. There is a subpanel in the basement but it was for a long retired hot tub. The breaker for it outside is shut off. So I am trying to come up with a way to make this as easy as possible but yet safe.
If your pug is grounded and you connect the ac in neutral and out neutral together and the grounds together you will be bonded if you are using a plug or not
 