Here are the ModBus Maps for these Conext Devices, XW/XW+ , Microsoft Onelink shared below and attached to this thread:
SE Devices OneDrive Link PDF’s - Below:
503-0244-01-01_RevA.4_Modbus_Map_Conext_SW_Device.pdf
503-0245-01-01_RevA.4_Modbus_Map_Freedom_SW_Device.pdf
503-0246-01-01_RevA.4_Modbus_Map_Conext_XW_Device.pdf
503-0247-01-01_RevA.4_Modbus_Map_AGS_Device.pdf
503-0248-01-01_RevA.4_Modbus_Map_MPPT60_Device.pdf
503-0250-01-01_RevA.4_Modbus_Map_GridTie_Device.pdf
503-0251-01-01_RevA.4_Modbus_Map_SCP_Device.pdf
503-0252-01-01_RevA.4_Modbus_Map_MPPT80_Device.pdf
503-0253-01-01_RevA.4_Modbus_Map_ConverterComBox_Device.pdf
503-0261-01-01_RevA.4_Battery_Monitor_Device.pdf
503-0262-01-01_RevA.4_Freedom Sequence Device.pdf
configuration.yaml
OK, So is anyone integrating the 6.8K into their setup using closed loop communication with their EG4 batteries? I am trying to get SOC to show up in my HA setup. I can get anything else, except that. My insight Local, says my slave address for the BMS is 230, but that address is dead.
Anyone have any success?
SE Devices OneDrive Link PDF’s - Below:
503-0244-01-01_RevA.4_Modbus_Map_Conext_SW_Device.pdf
503-0245-01-01_RevA.4_Modbus_Map_Freedom_SW_Device.pdf
503-0246-01-01_RevA.4_Modbus_Map_Conext_XW_Device.pdf
503-0247-01-01_RevA.4_Modbus_Map_AGS_Device.pdf
503-0248-01-01_RevA.4_Modbus_Map_MPPT60_Device.pdf
503-0250-01-01_RevA.4_Modbus_Map_GridTie_Device.pdf
503-0251-01-01_RevA.4_Modbus_Map_SCP_Device.pdf
503-0252-01-01_RevA.4_Modbus_Map_MPPT80_Device.pdf
503-0253-01-01_RevA.4_Modbus_Map_ConverterComBox_Device.pdf
503-0261-01-01_RevA.4_Battery_Monitor_Device.pdf
503-0262-01-01_RevA.4_Freedom Sequence Device.pdf
configuration.yaml
YAML:
# Loads default set of integrations. Do not remove.
default_config:
# Load frontend themes from the themes folder
frontend:
themes: !include_dir_merge_named themes
# Text to speech
tts:
- platform: google_translate
automation: !include automations.yaml
script: !include scripts.yaml
scene: !include scenes.yaml
sensor: !include sensors.yaml
influxdb:
host: a0d7b954-influxdb
port: 8086
database: homeassistant
username: homeassistant
password: homeassistant
max_retries: 3
default_measurement: state
modbus:
- name: conext_gateway
type: tcp
host: 192.168.86.245
port: 503
delay: 2
timeout: 15
#Always double check your address for each device.
#conext_gateway Device over MODBUS: XW Pro 6848 Bus ID 1, Bus address 0, Modbus SlaveAddress 10 (Port 502/503)
sensors:
#############
# - name: "Load AC Power"
# data_type: uint32
# unit_of_measurement: W
# scale: 1
# slave: 90
# address: 132
# device_class: energy
# - name: "AC Input Power"
# data_type: uint32
# unit_of_measurement: W
# scale: 1
# slave: 90
# address: 100
# device_class: energy
# - name: "Charge DC Power"
# data_type: uint32
# unit_of_measurement: W
# scale: 1
# slave: 90
# address: 92
# device_class: energy
#
# - name: "Load Output Energy Today"
# data_type: uint32
# unit_of_measurement: kWh
# scale: 0.001
# precision: 1
# slave: 90
# address: 220
# device_class: energy
# state_class: total_increasing
#
#
# - name: "Energy From Battery This Hour"
# data_type: uint32
# unit_of_measurement: kWh
# scale: 0.001
# precision: 1
# slave: 90
# address: 144
# device_class: energy
# state_class: total_increasing
#
#
# - name: "Energy to Battery This Hour"
# data_type: uint32
# unit_of_measurement: kWh
# scale: 0.001
# precision: 1
# slave: 90
# address: 168
# device_class: energy
# state_class: total_increasing
# - name: "Generator Status"
# data_type: uint16
# scale: 1
# slave: 51
# address: 77
# device_class: energy
#
# - name: "Generator to Battery This Hour"
# data_type: uint32
# unit_of_measurement: kWh
# scale: 0.001
# precision: 1
# slave: 90
# address: 192
# device_class: energy
# state_class: total_increasing
###############
# - name: "EG4 Internal BMS - Battery SOC"
# data_type: uint32
# unit_of_measurement: V
# scale: 1
# slave: 230
# address: 70
- name: "XW 4868 Inverter Enabled"
data_type: uint16
input_type: input
slave: 10
address: 71
- name: "XW 4868 Active Faults Flag"
data_type: uint16
input_type: input
slave: 10
address: 75
- name: "XW 4868 Active Warnings Flag"
data_type: uint16
input_type: input
slave: 10
address: 76
- name: "XW 4868 Battery Current"
data_type: int32
input_type: input
count: 2
slave: 10
address: 82
unit_of_measurement: A
scale: 0.001
offset: 0
precision: 3
- name: "XW 4868 Battery Power"
data_type: int32
input_type: input
count: 2
slave: 10
address: 84
scale: 1
offset: 0
precision: 0
device_class: energy
unit_of_measurement: W
- name: "XW 4868 Battery Temperature"
data_type: uint16
input_type: input
slave: 10
address: 86
unit_of_measurement: degC
scale: 0.01
offset: -273
precision: 2
- name: "XW 4868 Inverter Status"
data_type: uint16
input_type: input
slave: 10
address: 122
- name: "XW 4868 Load AC Voltage"
data_type: uint32
input_type: input
count: 2
slave: 10
address: 140
unit_of_measurement: V
scale: 0.001
offset: 0
precision: 3
- name: "XW 4868 Load AC Current"
data_type: int32
input_type: input
count: 2
slave: 10
address: 150
unit_of_measurement: A
scale: 0.001
offset: 0
precision: 3
- name: "XW 4868 Load AC Frequency"
data_type: uint16
input_type: input
slave: 10
address: 152
unit_of_measurement: Hz
scale: 0.01
offset: 0
precision: 2
- name: "XW 4868 Load AC Power"
data_type: int32
input_type: input
count: 2
slave: 10
address: 154
unit_of_measurement: W
scale: 1
offset: 0
precision: 0
scan_interval: 1
###
###
###
#conext_gateway device over Modbus: MPPT600/100 0 - Bus ID:1, Bus address:1, Modbus Slave Address (Port 503): 170
###
###
###
- name: "0 - MPPT100/600 100/600 Device State"
data_type: uint16
input_type: input
slave: 170
address: 64
- name: "0 - MPPT100/600 Charger Enabled Status"
data_type: uint16
input_type: input
slave: 170
address: 65
- name: "0 - MPPT100/600 Charge Mode Status"
data_type: uint16
input_type: input
slave: 170
address: 67
- name: "0 - MPPT100/600 100/600 Active Faults"
data_type: uint16
input_type: input
slave: 170
address: 68
- name: "0 - MPPT100/600 Active Warnings"
data_type: uint16
input_type: input
slave: 170
address: 69
- name: "0 - MPPT100/600 PV Input Voltage"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 76
unit_of_measurement: V
scale: 0.001
offset: 0
precision: 3
- name: "0 - MPPT100/600 PV Input Current"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 78
unit_of_measurement: A
scale: 0.001
offset: 0
precision: 3
- name: "0 - MPPT100/600 PV Input Power"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 80
scale: 1.0
offset: 0
precision: 0
device_class: energy
unit_of_measurement: W
- name: "0 - MPPT100/600 Battery Temperature"
data_type: uint16
input_type: input
slave: 170
address: 86
unit_of_measurement: degC
scale: 0.01
offset: -273
precision: 2
- name: "0 - MPPT100/600 PV Output Voltage"
data_type: int32
input_type: input
count: 2
slave: 170
address: 88
unit_of_measurement: V
scale: 0.001
offset: 0
precision: 3
- name: "0 - MPPT100/600 PV Output Current"
data_type: int32
input_type: input
count: 2
slave: 170
address: 90
unit_of_measurement: A
scale: 0.001
offset: 0
precision: 3
- name: "0 - MPPT100/600 PV Output Power"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 92
scale: 1
offset: 0
precision: 0
device_class: energy
unit_of_measurement: W
- name: "0 - MPPT100/600 Energy From PV This Hour"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 112
unit_of_measurement: kWh
scale: 0.001
offset: 0
precision: 3
- name: "0 - MPPT100/600 PV Input Active This Hour"
data_type: uint32
input_type: input
count: 2
slave: 170
address: 114
unit_of_measurement: s
scale: 0.001
offset: 0
precision: 3
OK, So is anyone integrating the 6.8K into their setup using closed loop communication with their EG4 batteries? I am trying to get SOC to show up in my HA setup. I can get anything else, except that. My insight Local, says my slave address for the BMS is 230, but that address is dead.
Anyone have any success?
Attachments
-
503-0244-01-01_RevA.4_Modbus_Map_Conext_SW_Device.pdf116 KB · Views: 6
-
503-0261-01-01_RevA.4_Battery_Monitor_Device.pdf93.7 KB · Views: 9
-
503-0253-01-01_RevA.4_Modbus_Map_ConverterComBox_Device.pdf133.7 KB · Views: 5
-
503-0252-01-01_RevA.4_Modbus_Map_MPPT80_Device.pdf104.7 KB · Views: 4
-
503-0251-01-01_RevA.4_Modbus_Map_SCP_Device.pdf80.6 KB · Views: 4
-
503-0250-01-01_RevA.4_Modbus_Map_GridTie_Device.pdf89.1 KB · Views: 5
-
503-0248-01-01_RevA.4_Modbus_Map_MPPT60_Device.pdf104.5 KB · Views: 5
-
503-0247-01-01_RevA.4_Modbus_Map_AGS_Device.pdf107.3 KB · Views: 4
-
503-0246-01-01_RevA.4_Modbus_Map_Conext_XW_Device.pdf160.2 KB · Views: 8
-
503-0245-01-01_RevA.4_Modbus_Map_Freedom_SW_Device.pdf127.5 KB · Views: 5