Almost burnt my house down...

esands

New Member
Joined
Sep 12, 2024
Messages
33
Location
Clinton Washington
I've just purchased the EG4 6000XP, 3 EG4 LL batteries and the 3 battery rack mount. I had professionally installed a Generic Manual Transfer Switch.
I have from my house main panel a 50 AMP breaker to supply power to the 6000XP. The load is installed in the Transfer Switch for it's gen input. The power to the transfer switch from the grid is connected to an second 50 AMP breaker in the main house panel.

All the cables from the panel to the 6000XP Are from a 50' string 8/4 SOOW pure copper UL-62 compliant cable. Black to L1 and Red to L2 Yes I have each leg grounded and natural on the 6000XP bus bars.

When I tested to see if everything is working, I killed the main 200 AMP main panel breaker. Lights out. Powered up the Batteries, and the 6000XP Turned on the Load that goes to the Transfer switch. All looked good.

When I hit the switch to cut over from grid setting to Gen on the transfer switch horrible noises house had an electrical fire smell. Needless to say I shut down the 6000XP as fast as I could. In my office where I have all my computer equipment a power strip was not fully melted but a melted hole on the bottom and very black.

What do we think? Bad Transfer Switch install, Defected Transfer switch, or defective 6000XP.
 
What do we think? Bad Transfer Switch install, Defected Transfer switch, or defective 6000XP.
I think you need to contact them and send it back for assessment rather than everyone speculating what could have happened without sufficient information. Please keep us updated.
 
Pictures...
 

Attachments

  • Main Panel-200AMP.jpg
    Main Panel-200AMP.jpg
    15.5 KB · Views: 187
  • PowerStrip1.jpg
    PowerStrip1.jpg
    28.1 KB · Views: 186
  • PowerStrip2.jpg
    PowerStrip2.jpg
    23.8 KB · Views: 186
  • Transfer Switch.jpg
    Transfer Switch.jpg
    16.2 KB · Views: 187
Where are the neutral wires switched??

When you switch from grid to the inverter, you also have to switch from using the neutral from the grid transformer to a neutral from the inverter. Not doing this makes the neutral open circuit and then the 120V loads can imbalanced, for example you could have 180V and 60V instead of 120V/120V, all depends on the 120V loads.
 
of your inverter wiring
Load connection goes to the inside of the Transfer Switch in the Gen Port. The Grid connection goes to my main home panel into a 50 amp breaker.
Black is installed as L1, Red as L2.

Looking at the picture of the Transfer switch, the top connections are from the Grid (Main panel 50 amp breaker) bottom is from the 6000XP Load.
 

Attachments

  • Inverter Bat.jpg
    Inverter Bat.jpg
    17.9 KB · Views: 143
  • Load-Grid.jpg
    Load-Grid.jpg
    21 KB · Views: 143
  • Inside of the switch.png
    Inside of the switch.png
    78.6 KB · Views: 144
Need this picture specifically.

Where is the transfer switch exactly?

Picture of inside the transfer switch?

It really sounds like the inverter OUTPUT was somehow connected to grid power.
I don't see how that could have happened with the main house panel 200 amp breaker off. I know this to be true as all power to the house was off.
 
Trying again, can you get a better picture of your load-grid connections? I can't tell from the angle, just want to make sure L1/L2 are correct and with the bends of the cable it's hard to see. Looking to verify that and your neutral connections.

Without opening the transfer switch (and I understand your reasoning), might be difficult for us to help further, until we see.
 
Please take a closeup picture of the Neutral bus bar in the 6000xp. I see you have your Neutral wire going to the first spot on the left after the mounting screw. That's usually where the internal 6000xp Neutral wire is connected.
 
Please take a closeup picture of the Neutral bus bar in the 6000xp. I see you have your Neutral wire going to the first spot on the left after the mounting screw. That's usually where the internal 6000xp Neutral wire is connected.
 

Attachments

  • Ground Bus Bar.jpg
    Ground Bus Bar.jpg
    17.5 KB · Views: 107
  • Neutral Buss Bar.jpg
    Neutral Buss Bar.jpg
    20 KB · Views: 109
The input and output of the 6000xp must not exceed 25A...

Likely nothing to do with the failure, but something to understand.
 
I don't see the 6000xp's internal Neutral wire connected to the Neutral bus bar. Take a closer look on the top side of that bar for a loose wire. It has a ferrule on the end.
 