Before I get deeper into this solar adventure I would like to hear if I'm doing it correctly.
European setup, 230v grid, mono phase, max load on the house 4500watts. It can happen however that the wifu goes apesh*t and turns everything on and I've seen occasional loads of 7000 watts (this happens when the baby soils the bed and therefore the washer, dryer and sterilzation equipement is turned on at the same time -- that does not happen frequently, but it can happen)
Here's what I have; 9 panels, the panels were free for me and they are brand new. They are Longi Solar 455wp, product number: LR4-72HPH-455M.
These are already installed, I've set them on the ground under a 36degree angle facing south. They are about 40 meters (single run) in cable removed from where the inverter will be installed. Cable is 4mm2. I measure 430volts or thereabouts on a sunny day OC.
Because of reasons I'm looking to get an off grid inverter, I do not want to send anything back into the grid, if I do send power to the grid the government has all kinds of annoying paperwork and regulations that i do not want to deal with. THey'll want to change my meter, I'll have to re-certify the whole electrical installation, just because.
The Growatt spf5000es looks really good. It would be able to cover the normal load, but the apesh*t load of 7000 watts would .. would what? I dunno, does it cut back to the grid at that point or does it just cut out completly? IF it cuts out completly I would need to get a second one.
With the panels all in series connected to the Growatt, I should be fine, right?
It does freeze in this country, does that mean I could get into trouble with the voltage?
What are my options then? Maybe I get another panel and do 2p5s? The datasheet on the Growatt does not mention the max amperage input ( datasheet: https://www.estg.eu/nl-nl/amfile/file/download/file/4296/product/3618/ ). I read on this forum that it's 18A and newer models do 22A. I think I would be delivered a newer unit and therefore with 10.92A (x2) STC rating I should be fine.
Now for batteries, I've ordered 16 EVE cells, 304AH from Amy, that should give me 15,5kwh and get me trough the nights on battery without depleting them completely each night. Night load is 1kwh.
Ok .. so what's wrong with this setup?
cheers
Before I get deeper into this solar adventure I would like to hear if I'm doing it correctly.
European setup, 230v grid, mono phase, max load on the house 4500watts. It can happen however that the wifu goes apesh*t and turns everything on and I've seen occasional loads of 7000 watts (this happens when the baby soils the bed and therefore the washer, dryer and sterilzation equipement is turned on at the same time -- that does not happen frequently, but it can happen)
Here's what I have; 9 panels, the panels were free for me and they are brand new. They are Longi Solar 455wp, product number: LR4-72HPH-455M.
These are already installed, I've set them on the ground under a 36degree angle facing south. They are about 40 meters (single run) in cable removed from where the inverter will be installed. Cable is 4mm2. I measure 430volts or thereabouts on a sunny day OC.
Because of reasons I'm looking to get an off grid inverter, I do not want to send anything back into the grid, if I do send power to the grid the government has all kinds of annoying paperwork and regulations that i do not want to deal with. THey'll want to change my meter, I'll have to re-certify the whole electrical installation, just because.
The Growatt spf5000es looks really good. It would be able to cover the normal load, but the apesh*t load of 7000 watts would .. would what? I dunno, does it cut back to the grid at that point or does it just cut out completly? IF it cuts out completly I would need to get a second one.
With the panels all in series connected to the Growatt, I should be fine, right?
It does freeze in this country, does that mean I could get into trouble with the voltage?
What are my options then? Maybe I get another panel and do 2p5s? The datasheet on the Growatt does not mention the max amperage input ( datasheet: https://www.estg.eu/nl-nl/amfile/file/download/file/4296/product/3618/ ). I read on this forum that it's 18A and newer models do 22A. I think I would be delivered a newer unit and therefore with 10.92A (x2) STC rating I should be fine.
Now for batteries, I've ordered 16 EVE cells, 304AH from Amy, that should give me 15,5kwh and get me trough the nights on battery without depleting them completely each night. Night load is 1kwh.
Ok .. so what's wrong with this setup?