North01
New Member
I'm looking to build upon Will's 5000w SunGoldPower handtruck system, also taking into account boflyer's recent modifications for full 5000w output. Thanks to 420hmsPA for his input on that thread - just looking to get as much input on this before I finally pull the trigger in the next week or so.
Quick background - I'll be building a small shed to house the Sungold and batteries - then running heavy duty extension cord to a trailer and yurt. No AC, wood heat, propane fridge in trailer. Main draws would be a well pump (looking at RPS, Vevor, etc), 120V washer/dryer, WiFi, laptop, lights etc. Should all be well within the Sungold's capacity - but we're in PNW and will be supplementing with generator in the winters as needed.
My biggest questions at this point are on wiring sizing, and if I need any added layer of protection (breaker/fuses) in the battery connection, as I'll be running 4 x 12v lead acids in series for the initial build - I know LiFePo4 batteries have built in BMS and breakers. The wiring specifications section of the SunGold manual (pasted below) says a 2P 200A breaker for the battery side, would this be fitting? -
I also have some DC breaker sizing and model questions - any pertinent difference between these two DiHool breakers for the PV panel disconnect switch? -
If 25A is recommended in the manual I should opt for 30A, even if my calculations regarding the ISC of the in series panel string only came out to 16.146 (10.35 ISC x 1.56 = 16.146), correct?


Rough diagram of the build - not sure if this adds any pertinent context for you all, but it was helpful for me to visualize.
Hoping for some confirmation on these wiring sizes, all should be pretty minimal length runs -
12 AWG from panels to DC breaker
4 AWG from DC breaker to inverter
2 AWG from Inverter to battery bank (likely with extra breaker added in this stretch) - on the other thread 420hmsPA mentioned he thought this should be upsized - any thoughts on how much?

Wiring section from the Sungold manual -

Thank you all for reading and any input you may have!
Quick background - I'll be building a small shed to house the Sungold and batteries - then running heavy duty extension cord to a trailer and yurt. No AC, wood heat, propane fridge in trailer. Main draws would be a well pump (looking at RPS, Vevor, etc), 120V washer/dryer, WiFi, laptop, lights etc. Should all be well within the Sungold's capacity - but we're in PNW and will be supplementing with generator in the winters as needed.
My biggest questions at this point are on wiring sizing, and if I need any added layer of protection (breaker/fuses) in the battery connection, as I'll be running 4 x 12v lead acids in series for the initial build - I know LiFePo4 batteries have built in BMS and breakers. The wiring specifications section of the SunGold manual (pasted below) says a 2P 200A breaker for the battery side, would this be fitting? -

I also have some DC breaker sizing and model questions - any pertinent difference between these two DiHool breakers for the PV panel disconnect switch? -
If 25A is recommended in the manual I should opt for 30A, even if my calculations regarding the ISC of the in series panel string only came out to 16.146 (10.35 ISC x 1.56 = 16.146), correct?


Rough diagram of the build - not sure if this adds any pertinent context for you all, but it was helpful for me to visualize.
Hoping for some confirmation on these wiring sizes, all should be pretty minimal length runs -
12 AWG from panels to DC breaker
4 AWG from DC breaker to inverter
2 AWG from Inverter to battery bank (likely with extra breaker added in this stretch) - on the other thread 420hmsPA mentioned he thought this should be upsized - any thoughts on how much?

Wiring section from the Sungold manual -

Thank you all for reading and any input you may have!