Hi,
I have two 260 watt panels, paralleled to a 40 amps epever tracerBN(mppt), connected to a diy 280ah lifepo4 battery.
The battery is at a low SOC, it's a sunny California day at around noon.
I'm getting 17 amps max :-\
I check the voltage at the panels, it reads approx 31 volts. (Vmpp = 30.7)
I check the voltage at the solar panel leads to the charge controller (when unplugged), it reads approx 31 volts.
I plug in the panel leads into the charge controller, voltage goes to ~26 volts, both with multimeter and the mt50 display.
(is this normal for voltage to drop when connected to the charge controller?, my wires are kind of chincey but would voltage drop only be present when connected or wouldn't it be lower when testing it unplugged, if that makes sense?)
I tested the short circuit amps of a panel, it's showing 7.5A (I may have to retest this due to undersized multimeter fuse issue)... (Panel rated current = 8.50 A, Short circuit current = 9.01 A)
I tried to configure the charge controller, but I may have to redo this, and I have yet to connect the PC to gain full access to the settings.
My thinking is that since the panels are reading close to rated voltage, and the short circuit amps is..fairly close.. to the short circuit current, that means the panels are OK, right?
Now, could my chincey wire be causing all this issue? I think they're CORRECTION 14awg CCA ( 16ft) but I'm running all four wires to the charge controller atm and paralleling them at the terminals... The issue persists with only 1 panel plugged in, i'll be lucky to get 9 amps..
The battery bms is a JBD 150A, the settings are right to accept a great deal more than 40 amps.
I think I've got 8 gauge wire(1-2ft) going from solar charge controller to battery, and 4 gauge (1-2 ft)going battery to inverter.. No change when under load..
Only other thing I can think of is that I had the charge controller connected to a lead acid battery before my lifepo.. but the same current was happening (I had thought it was because of limitations of the lead acid, but that is obviously not the case.
The converted voltage for the battery I think is reading 13.9v and 9a for one panel. Just about exactly twice the amps for two panels..
So I'm basically getting half the wattage out of the panels.. but whyyyy!!??
Thanks,
-mus
Ps: a couple of edits later and I'm honing in on the 16ft, 14awg, CCA mc4 wires I got off amazon as being the likely culprit. I'm going to cut them and temporarily rewire so that they are much closer to the charge controller and see if that has an effect.
I have two 260 watt panels, paralleled to a 40 amps epever tracerBN(mppt), connected to a diy 280ah lifepo4 battery.
The battery is at a low SOC, it's a sunny California day at around noon.
I'm getting 17 amps max :-\
I check the voltage at the panels, it reads approx 31 volts. (Vmpp = 30.7)
I check the voltage at the solar panel leads to the charge controller (when unplugged), it reads approx 31 volts.
I plug in the panel leads into the charge controller, voltage goes to ~26 volts, both with multimeter and the mt50 display.
(is this normal for voltage to drop when connected to the charge controller?, my wires are kind of chincey but would voltage drop only be present when connected or wouldn't it be lower when testing it unplugged, if that makes sense?)
I tested the short circuit amps of a panel, it's showing 7.5A (I may have to retest this due to undersized multimeter fuse issue)... (Panel rated current = 8.50 A, Short circuit current = 9.01 A)
I tried to configure the charge controller, but I may have to redo this, and I have yet to connect the PC to gain full access to the settings.
My thinking is that since the panels are reading close to rated voltage, and the short circuit amps is..fairly close.. to the short circuit current, that means the panels are OK, right?
Now, could my chincey wire be causing all this issue? I think they're CORRECTION 14awg CCA ( 16ft) but I'm running all four wires to the charge controller atm and paralleling them at the terminals... The issue persists with only 1 panel plugged in, i'll be lucky to get 9 amps..
The battery bms is a JBD 150A, the settings are right to accept a great deal more than 40 amps.
I think I've got 8 gauge wire(1-2ft) going from solar charge controller to battery, and 4 gauge (1-2 ft)going battery to inverter.. No change when under load..
Only other thing I can think of is that I had the charge controller connected to a lead acid battery before my lifepo.. but the same current was happening (I had thought it was because of limitations of the lead acid, but that is obviously not the case.
The converted voltage for the battery I think is reading 13.9v and 9a for one panel. Just about exactly twice the amps for two panels..
So I'm basically getting half the wattage out of the panels.. but whyyyy!!??
Thanks,
-mus
Ps: a couple of edits later and I'm honing in on the 16ft, 14awg, CCA mc4 wires I got off amazon as being the likely culprit. I'm going to cut them and temporarily rewire so that they are much closer to the charge controller and see if that has an effect.