You have switched to much lower voltage panels: 20.23V. 4 in series is only 81V vs. 150V limit.
That panel manufacturer uses a different convention. They're not using a %, they're using absolute voltage. -.08V/°C. So if it's 10°C cooler, the panel is 0.8V higher.
.08V/20.23Voc = .39% - close enough to 0.33% for me as a sanity check