I already have a 12V system set up at my off grid cabin. I want to change my solar array. I have a aims ssc-60a mppt charge controller and want to put 6 panels up. All 400 watt. 3 in a series then the 2 series paralleled together.
Each panel has a VOC 37.07V and ISC of 13.79 amps.
I rounded up to come up with 2 strings 120V and 14Amps parelelled together giving me 120v at 28amps. The operating volts on charge controller are 5-150V and amps is 60 amps.
To me this makes sense but the tech at AIMS is saying that 800 watt array is as big as I can use. Seems like it would be very difficult to hit 60 amps with a 800 watt array.
Any help would be appreciated.
The new array is in prep for new 48V system coming in a year or two.
Each panel has a VOC 37.07V and ISC of 13.79 amps.
I rounded up to come up with 2 strings 120V and 14Amps parelelled together giving me 120v at 28amps. The operating volts on charge controller are 5-150V and amps is 60 amps.
To me this makes sense but the tech at AIMS is saying that 800 watt array is as big as I can use. Seems like it would be very difficult to hit 60 amps with a 800 watt array.
Any help would be appreciated.
The new array is in prep for new 48V system coming in a year or two.