Hedges
I See Electromagnetic Fields!
- Joined
- Mar 28, 2020
- Messages
- 20,535
You may have difficulty replacing the battery in the middle of the apocalypse, so would be good to save its cycle life for then.
Consider chart on last page of this manual:
At 50% DoD, 1000 cycles. In three years it will be worn out if you let it cycle to that point every night.
Compare to 10 year float life.
I use these batteries (8x L16 size 6V 405 Ah) in a grid-backup system. Batteries are kept at float so long as grid is up. Grid down, GT PV responds to frequency shift, supplying power needed for loads and to keep battery at float or recharge if needed. Batteries only cycle if PV insufficient for loads, and at night.
I don't anticipate needing 650 cycles to 70% DoD out of them before they reach old age. If usage pattern did change I would try to cut off more loads at night, limit to 15% DoD for 3650 cycles. 4x inverter idle consumption of 100W over 12 hours would be 6% DoD, might be able to cut that to 3% with 3 out of 4 sleeping and an auto-transformer to create missing phase.
Consider chart on last page of this manual:
At 50% DoD, 1000 cycles. In three years it will be worn out if you let it cycle to that point every night.
Compare to 10 year float life.
I use these batteries (8x L16 size 6V 405 Ah) in a grid-backup system. Batteries are kept at float so long as grid is up. Grid down, GT PV responds to frequency shift, supplying power needed for loads and to keep battery at float or recharge if needed. Batteries only cycle if PV insufficient for loads, and at night.
I don't anticipate needing 650 cycles to 70% DoD out of them before they reach old age. If usage pattern did change I would try to cut off more loads at night, limit to 15% DoD for 3650 cycles. 4x inverter idle consumption of 100W over 12 hours would be 6% DoD, might be able to cut that to 3% with 3 out of 4 sleeping and an auto-transformer to create missing phase.