I didn't realize the shunt could control output. I don't currently have a shunt tied into My sunny islands, or any DC chargersThe 50 amp is the limit for the shunt reading not the grid so far as I can tell from experimenting this morning. After I got the shunt reading I could change the settings live and it would adjust. That said it is only reading half of the load going into / out of the battery.
The reason it was dumping the full load of the SB into the battery is it didn't see the shunt reading ... which is odd ... you think the default would be to NOT do anything if it can't see the shunt properly when ramping up / down in power. I had previously wired this to bypass that shunt and just used it as a big terminal block to bridge two wires on one post of the shunt.
So I need to rewire these units as the shunt is currently setup to only read off one of the SI's. This will likely mean finding another scrap shunt to use in place of the current one in the master load center so I can use it as a terminal block and migrating the one which came with the MN load center to be in series right at the BMS terminal block, and then shifting the two negative wires over as they currently split at the BMS shunt to each unit.