Glad to see that 14.5v
Awesome. Each time I do that on something I figure it's for the last time. Then it isn't. Hopefully you'll be good to go for a long while now.Just got done rewiring EVERYTHING.
I didn't follow this part. Do you mean you don't have all your charge and load + and - connections to the same terminals on your battery bank?I have the water pump wired DC to a battery in the middle.
I checked on it constantly as I was installing flooring in the living area. At one point when the sun jumped out from behind the clouds it peaked at 13.8 but never got back to the 14.x range. It was super cloudy all day both days though, so when I had it down to 12.3 the first morning after it hit 14.5, I was happy with it. Then each day it got back to 13.4 or 13.5 despite not much sun.NICE!
Hopefully, you witnessed a foray into the 14.XV range again, though it can be easy to miss if you're not trying to catch it.
Ceiling fans are off-grid banes. They use a lot of energy. They're particularly bad because everyone thinks, "hey, these things save energy," so they don't turn them off when not in use. A typical ceiling fan on medium can consume over 50% of your 190Ah capacity in 24 hours. 12.1V under a low load is getting close to the 50% threshold.
400W/12V = 33.3A peak
33.3A peak is a good charge current for 222 (15% charge current) to 333Ah (10% charge current) of batteries, so going for 290Ah is good if you get the 4th panel.
The coffee maker peaks at 895w. The Inverter is 1000w, and even when nothing else is drawing, the inverter shuts off when I run the coffee maker. It only takes 9 minutes to brew, and I always turn it off after brewing and keep the coffee hot on the furnace.Personally, given the low frequency of use, the type of stuff you're powering, and the cost, I'd put the PSW inverter off unless you find the inverter is actually unable to run the coffee maker... just long enough to run the brew cycle... not to keep it hot...
The coffee maker peaks at 895w. The Inverter is 1000w, and even when nothing else is drawing, the inverter shuts off when I run the coffee maker. It only takes 9 minutes to brew, and I always turn it off after brewing and keep the coffee hot on the furnace.
At the same time, I'm not sure I really looked at the bank at the time so it might have been low.
Next time the bank is in the 14.5v range I will give it a shot again.
The problem I foresee is that we'll almost always be running the coffee maker in the morning, and that will almost always be when the bank is at it's lowest charge. It's not the end of the world. We have a Coleman stove top coffee maker, so the electric one was just a luxury. At the same time, if I can make that work, it'll put this over the top as far as a success goes.
Our cabin is literally a half mile away from the nearest power line, so this system is a total victory for us.
Right now I've got about $1000 into it, and I plan on another $500 or so, and we'll be good to go.
I've been watching things a lot closer now, so I will have to keep that going and test the limits.If that's the case, a PSW might suffer the same fate. You upping your cable gauge recently will help a lot if that was the case. I'd definitely wait to try it on a day you KNOW you got to full charge the day prior and keep an eye on the voltage.
Lastly, I've probably mentioned it, but I've lost track. Even with the batteries indoors, when cold, they probably aren't being optimally charged unless you have voltage compensation active. If you have a temp sensor on your battery with compensation active. Stop reading. When it's 77°F or so, all the default numbers apply, but when its colder, charging voltage INcreases by 0.03V per 1°C, so if the batteries are at freezing the day before you get there, the charge voltage shouldn't be 14.5V, it should be 15.25V. If it's only charged to 14.5V at freezing, you might be leaving 10% on the table after a good day of sun, which means you might be starting with a lower charge when you arrive in the evening. Most chargers support this with a temperature probe.
Made a quick drive to the cabin today to plow the snow from this last storm.NICE!
Hopefully, you witnessed a foray into the 14.XV range again, though it can be easy to miss if you're not trying to catch it.