Hey everyone,
I'm hoping someone can advise on a solution to my issue.
I have a battery which was shipped to me without being top balanced in Cells 1,2,3 , these 3 cells have approx 25 percent more energy in them then the rest of the 1 cells. I have been monitoring these cells for 4 months and the issue remains just as it was the first time it ever charged to 100 percent.
The first 3 cells hit 3.62v and the other 13 never go above 3.4v as over voltage protection kicks in at 100 percent.
The BMS is a PaceEx 200A 16s 1P and the cells at EVE Grade A cells with QR codes to match, the issue is they are welded and are very difficult to access (3cm gap between a metal top plate that cannot be removed without completely disassembling the battery. The Pace bms only has a small passive balancer and could never deal with this inbalance and the supplier refuses to acknowledge an issue saying that it's normal at these high voltages and just to lower the charge threshold to get around it.
I had a 5A active balancer installed at the factory and it appears to do nothing when switched on by the button they provided, I left it on for 20 hrs at 100 percent and both Charge and Discharge mosfets turned off in the BMS and nothing changed other then the small amount of power drained naturally by the BMS being turned on so I could monitor the cells movements. I also tried this without the BMS on.
My only solutions that I can see, is to use some sort of long insulated probe to connect to each cell one by one to the positive and negative terminals in question and then draw down power using a 3.2v battery load capacity tester like the ZKE-Tech EBC-A20 until the cells voltages match those of the other cells or the other way around charge up all the cells to 3.65v ) this would take days as it would require 35/40AH per cell at 5A :-(
If someone has ever achieved this or done a similar method, can they advise on the device used to drain/charge the cells.
Can you also confirm that regardless of the cells being welded together that if I turn off the BMS and breaker, that if I connect the positive and negative of the discharger/charger that it will only charge/discharge the cell that it's connect to and not the other cells?
I'm hoping someone can advise on a solution to my issue.
I have a battery which was shipped to me without being top balanced in Cells 1,2,3 , these 3 cells have approx 25 percent more energy in them then the rest of the 1 cells. I have been monitoring these cells for 4 months and the issue remains just as it was the first time it ever charged to 100 percent.
The first 3 cells hit 3.62v and the other 13 never go above 3.4v as over voltage protection kicks in at 100 percent.
The BMS is a PaceEx 200A 16s 1P and the cells at EVE Grade A cells with QR codes to match, the issue is they are welded and are very difficult to access (3cm gap between a metal top plate that cannot be removed without completely disassembling the battery. The Pace bms only has a small passive balancer and could never deal with this inbalance and the supplier refuses to acknowledge an issue saying that it's normal at these high voltages and just to lower the charge threshold to get around it.
I had a 5A active balancer installed at the factory and it appears to do nothing when switched on by the button they provided, I left it on for 20 hrs at 100 percent and both Charge and Discharge mosfets turned off in the BMS and nothing changed other then the small amount of power drained naturally by the BMS being turned on so I could monitor the cells movements. I also tried this without the BMS on.
My only solutions that I can see, is to use some sort of long insulated probe to connect to each cell one by one to the positive and negative terminals in question and then draw down power using a 3.2v battery load capacity tester like the ZKE-Tech EBC-A20 until the cells voltages match those of the other cells or the other way around charge up all the cells to 3.65v ) this would take days as it would require 35/40AH per cell at 5A :-(
If someone has ever achieved this or done a similar method, can they advise on the device used to drain/charge the cells.
Can you also confirm that regardless of the cells being welded together that if I turn off the BMS and breaker, that if I connect the positive and negative of the discharger/charger that it will only charge/discharge the cell that it's connect to and not the other cells?