20k$ ..? 20kEuros ? 20kBananas ?Tis all about the potential 20K arc
It's possible that those fuses won't be able to extinguish an arc from a high power battery properly.
Class T's are used for a reason. You can get them on eBay WAY cheaper if you look. IIRC, I paid like $8 a fuse last time for "new, old stock".
I'm building my system and need to fuse the battery bank. 30kwh 48v
Class t fuses are super expensive, what do you think about these ? Way cheaper and I won't cry if I blow a fuse. thanks for your help !
InstallGear 0/2/4 Gauge Ga ANL Fuse Holder + 300 Amp ANL Fuses (2 Pack) View attachment 104463
Victron Mega exist in 58V48V system.
ANL is fine for 12V.
MEGA is only rated up to 32V, again 12V would be fine, on 24V I'd go Class T.
48V nominal voltage system, you need a Class T. Ebay or sites like this best prices and good quality T fuses, are reasonable. I have purchased from Best Converter and Ebay, no complaints.
A class T can interrupt 20,000 amps..... ANL fuses have an interrupt rating of 5000 Amps which by the ABYC standards allows them to be used as the primary circuit protection for large battery banks....
They do, if used in the Victron fuse holders. If price is a concern, I doubt a person would purchase Victron.Victron Mega exist in 58V
Source of the "easy" 5000A ? Cause i do not like to build my thinking on unreliable informations. (i'm not saying you are unreliable .. but i would like to know the source of this information)A class T can interrupt 20,000 amps.
There's small lithium banks that can EASILY push well over 5000 amps during a short. For a larger pack, 5000 amps can be within spec. Most of the time, the ANL fuse would probably be okay, but if your bank can put out more power then your fuses rating, you shouldn't be using that fuse.
Edit: I just sat you have a 30kwh, 48v bank. You need a class T.
I've never heard of those type of breakers before. It SAYS the AIC rating is 25,000 amps at 60vdc. UL listed too... ?You can get new DC breakers on Ebay pretty cheap. The specs are published on them for trip time vs amps. I think this was a medium. If it's a dead short it just trips. https://www.ebay.com/itm/222304797420
I have a 25 amp hour lithium cell that I was able to pull well over 600 amps out of. Go to Google and type in "calb grey cell test" that dude manages to pull over 2,000 amps out of a SINGLE cell. Your pack is SUBSTANTIALLY larger than that. Even if your bank was lead acid, a 30 kilowatt pack should be able to push 5,000 amps, no problem.Source of the "easy" 5000A ? Cause i do not like to build my thinking on unreliable informations. (i'm not saying you are unreliable .. but i would like to know the source of this information)
They are talking about 60V system which is not what we are looking for here, but the discussion in your link is informative, thanks.They do, if used in the Victron fuse holders. If price is a concern, I doubt a person would purchase Victron.
Find the AIC rating because they don't print it that I've been able to find.
One thing to remember is Victron indicates the MIDI, MEGA and ANL are fuses designed for downstream protection of individual circuits, not for overall system amperage protection. That is an important distinction, just like if there was a 300A MINI fuse manufactured, you wouldn't use it for overall system amperage protection. It wasn't designed for that purpose.
Read this from the Victron forums, especially the post by johnsmith regarding AIC MRBF fuse in Lynx distributor
A DC breaker is not a fuse,You can get new DC breakers on Ebay pretty cheap. The specs are published on them for trip time vs amps. I think this was a medium. If it's a dead short it just trips. https://www.ebay.com/itm/222304797420
I know the video, Damien did 2200A on a 180A LiFePo4 grey CalbI've never heard of those type of breakers before. It SAYS the AIC rating is 25,000 amps at 60vdc. UL listed too... ?
Most lithium cells can push out over 20c druing a short, some can probably do much more. 30kw / 48v = ~625ah. 625ah x 20c = ~12,000 amps of short current, minimum.
I've personally witnessed cells do much higher than that. I posted a video on here not too long ago on a shorted a 25 amp hour cell, and it maxed out my 200a amp clamp. I redid the test later with a 600a clamp, and it maxed it out as well.LFP can Burst discharge to 5C.
100A -> 500A
The question remain the same ... how much Amp can make a 300A LiFePo4 when shorted.