I have 24v system and the charger says 26.6 at the last beeping. Outback FM 60 controllerusually that happens when the battery gets to low charge.
26.6 could also be too high a voltage, but most 25V inverters operate up to 30VI have 24v system and the charger says 26.6 at the last beeping. Outback FM 60 controller
At 28.8V, the controller is near full, 1.1A is still charging them. The inverter specs are needed to help you further.My inverter has beeped and shut down 2 times this morning. 1 a 11:00am and 1 @ 12:00,
Very clear skies.
My controller reads
In 64.9v. 0.4a
Out 28.8v. 1.1a
,30kw. .07kWH
I shut down 1 of the circuit breakers.
Any ideas would help please.
I have a Outback FM 60. I will look for manual for the inverter. Giandel 2000w - 4000w model PS2000kAR.At 28.8V, the controller is near full, 1.1A is still charging them. The inverter specs are needed to help you further.
What brand and model is it? Do you have a manual for it, are there troubleshooting options in it?
at This point Anything we say is merely a guess...
None but 12v now having 110v installment this week. I’m not a electionHow much of a load are you putting on the inverter? What is the load? AC? Microwave?
High voltage cut out is 32V on that model... so, we need to know the beep codes to know what it is.I have a Outback FM 60. I will look for manual for the inverter. Giandel 2000w - 4000w model PS2000kAR.
will search Morning’s Thank you
Did you solve this issue with your set up? I believe I built the same set up 24V 2000W system. My 2000W- 4000W PURE SINE continuously beeps with TWO (12V 100Ah) series connected. However if I just use ONE ( 12V 100Ah ) Battery is works fine. If it is to high of a voltage with TWO is there a way to lower it a bit?
View attachment 22693
My inverter is 24v so 12v will not work. I am now plugged in my refrigerator and it says 28.8v out. I am going to check with Battle Born and ask themDoes your inverter really work on 24v as well as 12v?