Since your panels are in series, you can skip the fuse. A dual pole DC rated breaker can be used instead of the PV disconnect. But the use of the PV disconnect isn't wrong at all.
If you're putting the MRBF holder for the solar charge controller cable on the busbar, that's at the wrong end of the cable. The fuse or breaker for the solar charge controller should be as close to the solar charge controller as possible. For that position I like the
Blue Sea 285 breaker.
4/0 from each battery to the battery busbar is overkill. You could get by with 2/0. 4/0 after the battery busbar is appropriate. However, since your diagram doesn't include any distances, we don't know for sure if 2/0 is acceptable.
View attachment 262981
Instead of two battery switches, you could use just one between the battery busbar and the common busbar. The inverter should then connect to the common busbar not the battery busbar. The inverter would need to be fused, but it wouldn't have to be a Class T fuse.
Your 60 amp LiFePO4 charger is connected to the wrong busbar. Put it on the common busbar not the battery busbar. Otherwise, the shunt won't see the current going into the batteries and it will report a lower state of charge.