GoldenNoodle
New Member
- Joined
- Sep 30, 2021
- Messages
- 15
I kind of inherited a wind/solar setup. It's got a 400 watt 12v 'Whisper' wind turbine, 480 watts of 12 vdc panels in a mix of 80 and 120 watts and 10 x 110 AH deep cycle 'renewable energy' batteries. The charge controller looks like it's an OEM/no brand name. Probably PWM ?
The battery bank was replaced in November 2019.
In the November-March time frame the system needs to be topped up with a generator at least once a week, in December it's 2x a week.
There's a constant 35 watt draw.
When I (try to ) do the math on that I get 10 x110 = 1,100 AH * 50% = 550 AH @ 12v = 6,600 Watts / 35 Watt draw = 188 hours (?) So even if there is almost no power from the PV or the wind it should still run about 7.8 days ?
Does that seem "right" ?
If so then what is the best option to increase run time ? In terms of a ratio is the PV/Turbine sized properly to the battery capacity ? Should I add PV or storage or both ?
If the numbers are whacky then where might I look for gains in the system (replacing the PWM controller?).
As well I have a 24 vdc 240 watt panel that came along with a different acquisition - what are some thoughts on adding that to this system ?
Thx
.
The battery bank was replaced in November 2019.
In the November-March time frame the system needs to be topped up with a generator at least once a week, in December it's 2x a week.
There's a constant 35 watt draw.
When I (try to ) do the math on that I get 10 x110 = 1,100 AH * 50% = 550 AH @ 12v = 6,600 Watts / 35 Watt draw = 188 hours (?) So even if there is almost no power from the PV or the wind it should still run about 7.8 days ?
Does that seem "right" ?
If so then what is the best option to increase run time ? In terms of a ratio is the PV/Turbine sized properly to the battery capacity ? Should I add PV or storage or both ?
If the numbers are whacky then where might I look for gains in the system (replacing the PWM controller?).
As well I have a 24 vdc 240 watt panel that came along with a different acquisition - what are some thoughts on adding that to this system ?
Thx
.