BMS handling inverter peak

houdayec

New Member
Joined
Jun 23, 2021
Messages
8
Hi everyone,

I have recently purchased a 4x3.2v 280ah EVE cells to make my own battery on 12v.

However, I have some doubts about the max load of my BMS. Here's my situation:

I plan on using, sometimes, a 1000w inverter with a peak @ 2200w (183a) for a few seconds

At the same time, I will have an average of 30a connected equipments.

- Normal use would be: 83a (1000w/12v inverter) + 30a (equipments) = 113a -> in this case, a 150a would make a great job, without pushing to the limits
- Peak use would be: 183a (2200w/12v inverter) + 30a (equipments) = 213a -> 150a BMS would not be enough

What should I do? On normal usage, a 150a BMS is more than enough, but will it handle a 20s peak from the inverter?

Thanks in advance for your advices
 
Many BMS have good short (very short) duration tolerance of high surge currents.

If you actually expect to utilize your inverter's surge power, you should size the BMS for it.
 
Many BMS have good short (very short) duration tolerance of high surge currents.

If you actually expect to utilize your inverter's surge power, you should size the BMS for it.
I don't plan on using it. Thanks for your answer
 
If its a high frequency inverter you can safely ignore the surge capacity as its rated in milli-seconds.
 