I'm building two 48v 75 aHr LiFePo4 batteries that I will wire in parallel to a Growatt 3000ES hybrid inverter. I'm using 18" (one way) of 4awg. I'm trying to size a breaker/fuse just downstream of the battery bank. I'm confused by the calculations for determining fuse size. I will pull no more than 12a @ 120v from the inverter.
One suggestion is to use a Class T which seem to start at 200a.
Another suggestion was this calculation... 3000w / 48v * 1.25 = 78amp
And can I use a breaker like this - 63a double pole? Smseace 63a DP breaker
One suggestion is to use a Class T which seem to start at 200a.
Another suggestion was this calculation... 3000w / 48v * 1.25 = 78amp
And can I use a breaker like this - 63a double pole? Smseace 63a DP breaker