I have a sub panel going to fed by inverter, no generator or grid.
This was shipped bonded, I want to unbond it because my bond is elsewhere. Left bar is neutral and right bar is ground, do I remove both green bonding screws or an I right that only the left ( neutral) bond screw needs to be removed?
Also, I need to feed panel from right top two breakers? What's the reason for that?
@timselectric
1000002352.jpg
 
Remove the bonding screw in the left, have all your neutral on that bar, then all your grounds on the bar all the way to the right.

Check with your meter there’s no continuity between neutral bar and ground bar, or neutral and case.

So where are you bonding?
 
Remove the bonding screw in the left, have all your neutral on that bar, then all your grounds on the bar all the way to the right.

Check with your meter there’s no continuity between neutral bar and ground bar, or neutral and case.

So where are you bonding?
Thats what I thought, yes meter has no continuity now.
I have a 2 breaker box that's running now with a bond, I have to open it up and see if it's a pain to unbond, or might use the inverter bond.
 
I see two green neutral bonding screws (!) The ground bar is to the far right.
Check with an ohm-meter. Edit: ok you did
 
I see two green neutral bonding screws (!) The ground bar is to the far right.
Check with an ohm-meter.
Correct the instructions in the box are unclear but if I remove both the case is ungrounded which is not desirable.
 
Yet another dumb bonding question.
I have a sub panel going to fed by inverter, no generator or grid.
This was shipped bonded, I want to unbond it because my bond is elsewhere. Left bar is neutral and right bar is ground, do I remove both green bonding screws or an I right that only the left ( neutral) bond screw needs to be removed?
Also, I need to feed panel from right top two breakers? What's the reason for that?
@timselectric
View attachment 293955
Definitely remove the one on the left. Maybe the one on the right, I can't really see how it's in there.
Continuity testing will tell you for sure.
And yes, top right or left breaker will be the main breaker location.
 
It is the industry standard. But I don't know why it would matter.
Unless that panel only has provisions for locking the breaker in place, on the right side.
OK, there's no interlock or lockout. Couldn't find anything different between left and right location.
Also it shows that you only need to remove the left green screw.
You have one neutral bar (left). And two ground bars (right).
Correct but it said bonded, which I initially thought was part of the n-g bond but I assume it's bonded to case note.
 
OK, there's no interlock or lockout. Couldn't find anything different between left and right location.
A backfeed main breaker, must be affixed in place. There should be provisions for this. (A screw or clamping device, to physically hold the breaker in place)
 