Am I wrong in thinking that the most the amp flow could be is the max my inverter could draw?That is a LOT of current capability...
Be sure you size the bussbar for the amp flow.
900amp would be 1C...
Am I wrong in thinking that the most the amp flow could be is the max my inverter could draw?
Putting together a 3P4S bank with twelve 310Ah cells and a REC active BMS. I could use some help with Busbars. Will it be ok to buy 1/4" x 1" copper and make my own? Will the longer, 6 terminal lengths be a problem? Thanks in advance!
View attachment 45307
Safe assumption but size everything to handle the rating of the fuse. If you are using a 400A fuse make sure everything can handle that.
Also be cautious and plan how to limit potential for shorts between the cells, and between cells and the fuse. With 930Ah that is like a small Chernobyl if it shorts out and you can't stop it.
I would strongly suggest considering a fuse between the first 3P2S block and the second as well.
Fuses add heat (and resistance). You need one fuse per battery. Just size it properly. Putting one between cells will make readings from your BMS off. McMaster Carr carries busbar with reasonable shipping.
Reality is probably that you will be limited by available breaker size and wire size.Am I wrong in thinking that the most the amp flow could be is the max my inverter could draw?
I was wondering how it would effect the BMS... no fuse in between packs... Thanks!Fuses add heat (and resistance). You need one fuse per battery. Just size it properly. Putting one between cells will make readings from your BMS off. McMaster Carr carries busbar with reasonable shipping.
A quarter inch by one inch should be able to handle approximately 400 amps with a temperature rise of 30 degrees Celsius. So about 300 amps. The longer busbar should not be a problem, just keep the screw holes as small as possible/reasonable. You might want to consider 3 separate battery packs and BMS to give some redundancy. Even using contactors, you will have problems being able to handle 900 amps.Putting together a 3P4S bank with twelve 310Ah cells and a REC active BMS. I could use some help with Busbars. Will it be ok to buy 1/4" x 1" copper and make my own? Will the longer, 6 terminal lengths be a problem? Thanks in advance!
View attachment 45307
Good advice on making your own there. The wedding ring is something to watch out for, since there is easily enough amps to totally vaporize your ring. Not just get hot, but literally make it a cloud of rapidly expanding gas (aka explode).I have made Busbars with a drill press and with a handheld battery drill -- The handheld drill worked rather easy (surprisingly)
A machinist friend of mine showed me to put masking tape on the metal where I wanted to make my marks --then use a 1/8" bit just to make dimple in the metal --then drill the holes the size you need --- Slow is better and clamp your work down -- nothing worse than a spinning piece of bar stock
I use plenty of tape over all the terminals I'm not working on -- I had a mishap with my wedding band that taught me well ( millisecond short had my ring glowing and burnt a ring around my finger -- I decided to rotate my connections 90 degrees from your diagram -- therefore your pos and neg terminals are further apart -- this way you have two 3 hole busbars / two 3x3 square busbars / one 6 hole busbar
This image shows what the Everlander guy did. He's pretty sharp and typically well thought out designs so would not hesitate to copy this idea. It's also not a theoretical view as he's been all over with this system design. You can see the mega-fuse between bus bars in the bottom. His is a 5P4S design I believe.
View attachment 45337
The serial connection should carry 100% of the current you are using, parallel would only carry "balance" current.Curious, in a parallel/serial battery set-up what carries more current, the parallel or serial connection?
Volts the same, amperage is the same.Curious, in a parallel/serial battery set-up what carries more current, the parallel or serial connection?
how did this go?Putting together a 3P4S bank with twelve 310Ah cells and a REC active BMS. I could use some help with Busbars. Will it be ok to buy 1/4" x 1" copper and make my own? Will the longer, 6 terminal lengths be a problem? Thanks in advance!
View attachment 45307