Now that I know what kind of cells are in my 200Ah 12v CHINS battery:
GFB 3.2 V
320Wh
100Ah
48173125
OALCBA3510000D
A search online reveals the C rating
Looks like it is .5 C per cell.
There are 8 cells total making it 2 series 4 parallel I think.
Because it is a 200 Ah battery, if it were 1C it could discharge 200 amps in one hour if BMS would support it I believe.

If it were 2C rated cells it could consume 200 amps in 30 minutes I believe.

Therefore - and please correct me if I’m wrong - the .5 C rating of these cells should mean a discharge rate of no more than 100 amps per hour. Is that correct? Or I could drain it no faster than 100 amps over a two hour period from full to empty.

Does this sound right, or does having cells in series play a factor?

Honestly I didn’t know what to expect when opening it. I thought there would be 4 big batteries not 8.
 

Attachments

I should note that I also upgraded the BMS to support 150 amps. Existing one didn’t like anything over 50 amps continuous. Wondering if cells have something to do with that and not BMS.
 
You sound correct, apart from cells are arranged 2P4S.
Be aware of other limits such as min / max voltage / charge rates ect.
 
Also check if existing battery connections/ bus bars ect are capable of discharge / charge you intend if this is above what data sheet indicates.
As the designer / modifier it's down to you to ensure all is correct, ah the fun of responsibility 😉
 
I think:

If you take 4x 25Ah .5 C cells and put them in parallel they become a 100Ah .5 C cell.

25Ah @ .5 C =12.5A

100Ah @ .5 C =50A

It still take 2 hours to discharge at .5C. A .5C rated cell cannot be discharged within 1 hour within it's rated spec.
 
Also check if existing battery connections/ bus bars ect are capable of discharge / charge you intend if this is above what data sheet indicates.
As the designer / modifier it's down to you to ensure all is correct, ah the fun of responsibility 😉
The other equipment has been verified by folks on these forums. T class fuses and bus bars and conductor sizing and lugs etc all good.
 
I think:

If you take 4x 25Ah .5 C cells and put them in parallel they become a 100Ah .5 C cell.

25Ah @ .5 C =12.5A

100Ah @ .5 C =50A

It still take 2 hours to discharge at .5C. A .5C rated cell cannot be discharged within 1 hour within it's rated spec.
But they are 100Ah cells, not 25Ah.
 
The spec sheet says 1C continuous and up to 3C for 1 min.
So 1C * 100Ahr = 100A * 2(p) = 200A continuous.

The limiting factor is your BMS.
The spec sheet for the 100 Ah cells I attached says 1C continuous? Saw .5 continuous.

Oh, you are saying discharge is 1C. That is good to know. I was talking about charging. I’m sorry. Continuous looks like it is .5 C.

With that information, you believe I can do 100 amp discharge and 50 charge continuous, or are you saying 200 amp discharge and 100 amp charge is what the batteries can Support?

I realize the BMS is only for 150 amp discharge. The current BMS is only for 50 A current and 100 max.

I run a pool pump and pool heater that is about 95 A continuous for several hours.

I am hoping the issue was the BMS and not the cells.
 

Attachments

  • IMG_4167.png
    IMG_4167.png
    400.1 KB · Views: 6
  • IMG_4168.png
    IMG_4168.png
    353.2 KB · Views: 5
  • IMG_4169.png
    IMG_4169.png
    353.5 KB · Views: 5
Both charge and discharge at the single cell level is to 1C continuous. You have 2 in parallel so you can charge and discharge at 1C of 2x100 = 200A.

95A continuous for your battery would be = to .5C discharge.

Keep in mind though that most EOL ratings are at .5c or less so you may lose some cycles at higher C rates..
 
I have overlord cut off for charge and discharge set to 160 now. Is that good? I think I said it for two seconds before shutting down.
 
Please note that saying "per hour" is superflous.

Charge and discharge ratings have a time spec to them.

Per hour implies you are discussing storage or usage capacity or quantity.

And it is covered by the Ah spec, or the Wh/kWh spec...

Never a reason to say "per hour" unless you are discussing what your loads are...
 
A pool pump and a pool heater. It is happening by the way of an inverter. I have 5600 W and Solar, three different solar charge controllers, three different arrays, and have max current dialed way down.
 
Yes, I know I need more batteries. I am switching the inverter to 48 V soon which I already have. I just don’t have a 48 V battery yet. Quattro 48V 5000 already owned. Big MPPTs already.
 