So I just ordered an RUiXU RX-12K. Should be delivered next week. Starting to plan everything for the install but came across something that seemed strange in the manual.
For the connection to the Grid Panel it says to use a 100A breaker and 6awg cable.

This seems too small from everything I've read. It's only going to be a 3ft run but still seems off. Does this seem right? I would just do 4awg but I happen to have some spare 6awg THHN cable so would be nice if I can use it.
***************
EDIT:
These cable will be single in air and the reality it is highly unlikely it will get even close to 100A considering all my loads on my inverter will likely max out close to 45A.
So maybe I'd be fine with the 6awg but switching to a 60 or 75A breaker. The whole point of the breaker is to protect the cable right?
So if my theory is correct I'll install a 60 or 75A breaker which is fine got 6awg THHN, and if everything works we're good. But if the breaker trips, it tells my I should increase to a 100A breaker and increase the wire size too?
******************
For my battery I have 8x 12v 280ah I'm going to wire in a 4s2p config. I know it's not preferred to go 12V but I got them at a very good price. And I know lots have this config without issue.
My plan was to use busbars to form the 4S with a battery balancer, and 2/0 from the 2x 4S battery banks to a 500A distribution block. Then 2/0 from the block to the inverter. Does that sound right too? Or do I not need 2/0 to from the batteries?
Thanks for you advise.
Cam
For the connection to the Grid Panel it says to use a 100A breaker and 6awg cable.

This seems too small from everything I've read. It's only going to be a 3ft run but still seems off. Does this seem right? I would just do 4awg but I happen to have some spare 6awg THHN cable so would be nice if I can use it.
***************
EDIT:
These cable will be single in air and the reality it is highly unlikely it will get even close to 100A considering all my loads on my inverter will likely max out close to 45A.
So maybe I'd be fine with the 6awg but switching to a 60 or 75A breaker. The whole point of the breaker is to protect the cable right?
So if my theory is correct I'll install a 60 or 75A breaker which is fine got 6awg THHN, and if everything works we're good. But if the breaker trips, it tells my I should increase to a 100A breaker and increase the wire size too?
******************
For my battery I have 8x 12v 280ah I'm going to wire in a 4s2p config. I know it's not preferred to go 12V but I got them at a very good price. And I know lots have this config without issue.
My plan was to use busbars to form the 4S with a battery balancer, and 2/0 from the 2x 4S battery banks to a 500A distribution block. Then 2/0 from the block to the inverter. Does that sound right too? Or do I not need 2/0 to from the batteries?
Thanks for you advise.