Wanted to shared the work I did on my LV system for the sprinter van I am converting into a camper. The objective of this project was to have a stupid amount of power available with little loading effect, a high Energy to size ratio, field serviceable, and low cost. I have never done a system like this before but my background is an electrical engineer who does advising type work in commercial device manufacturing so I like to think I know my way around not blowing myself up and not setting myself on fire.

(Main) Parts Used:
3 - Tesla Model S Battery Module 5.2KwH
Victron Energy MultiPlus-II 24v
Overkill solar Tesla BMS kit – Plug-and-Play Retrofit Kit
Victron Energy Orion 24/12-70A DC-DC Converter
4AWG stranded pure copper wire (stripped out of a retired tesla supercharger station)

Metrics:
Battery box weight: 200lb
Total yield: 13-14 kwH (from initial test depleting 80-20% still benchmarking)
Batt box cost: $2000
System cost (including excluding solar parts): $3500
Labour time: (excluding solar work) 64.5 Hours

Explanation:

I Plan on doing a circuit diagram and full part list in a later post. But wanted to show the finished pictures and some of the construction shots I had to get feedback and comments on the forms.

The innovative thing I did here was really a racking system for the tesla battery modules. The intention was originally have support for a hot spare. but after realizing the 660W of solar panels I have mounted on the roof (plan to show that project in a different thread) has a less than expected average yield all 3 modules are relatively permanently installed. Batteries are mounted on 2ft long 1" 8020 extruded aluminum. I found that the extruded aluminum formed the best ridge for sliding the battery in and out of, as tesla's modules, as you can see by other builds do not have a good place to rack and mount really.

LiPo type batteries are typically discouraged in use with DIY vans so I had to factor in multiple failsafes.
Each module has a 150A block fuse, and the Overkill solar BMS that has 100A Efuse.
Each battery is then wired into a shutoff switch. This was an expensive edition with the partial operation under a single modules failure in mind, and removing batteries to charge them not with the van. Now that the sub-project is done, not sure if it was worth the hassle and wire.

Positive and negative of the battery box go into a box-side bus bar with 5 foot of extension into where the I/O is to be.

On the Inverter side, I have a MultiPlus-II 24v which should give me all the 120V power needed for electronics in the system and can do the 70 Amp shore connection charging. batt Box is connected to a 3 Pol switch so that the LV system and inverter can be switched on or off separately of each other.

There is then a bus bar for servicing the 24v LV appliances that go into the van and a Victron Orion 24/12-70A DC-DC Converter to step down the native 24v so that 12v appliances will work as well.

Things I am glad I did:

Use at least 24v, 12v systems are terrible because so much power is lost in transmission due to the twice as high current for the same power output. The $100 step down was an easy fix to not have to do a 12v system. I maybe would have done even a 48v if there was no solar involved, but that would need an even number of tesla modules.

Using the tesla modules, the yield on these is pretty friggin good considering the cells themselves cost me $300 a peice. They are IMO far safer than doing a DIY LiPo cell pack like I originally planned.

The 150A block fuses were cheap to add on, and gives me piece of mind that if a tool or the module itself fell in a way to make a full short outside the BMS's Efuse or if the Efuse failed, I would not incinerate my van.

Things I learned:

I got the overkill solar BMS for peace of mind, The Efuse gives me the assurance that from the lowest level the battery will shut off under a fault and I can better monitor the performance of each module. I originally did not design for it and could have done without that particular part it to save $600 on the batt box. I am not the most thrilled with the COTS-chinese main BMS with soldiered on wire but I will admit the new Pathfinder that is replacing this model looks like it is worth it and overkill benchmarks each of the COTS part of the BMS and provided a test report in the packaging. It really is just an optimization if I could have also done this part myself as it pained me to use a $200 BMS with each $300 battery pack. But I figure I could have at most saved $300 here after the cost to do something else not even to mention the time.

The per module disconnects I had big intentions for. The only time it came in handy was bringing up each module to synchronize voltages after they had drifted from keeping the batteries disconnected durning assembly. It was a pain to cap more wire, using the wire, and installing them. A nice to have feature, did not need to be done in phase one here.
I did not have access to a laser engraver to cut the acrylic so I did it with drills, circle cuts and a jig saws. I am glad this part is acrylic, but I will probably completely redo those with a laser engraver. It was a big waste of time and took away from the polished look of the batt box.

The extruded aluminum cost like $400, because I was impertinent and used mcmaster, I really could have used a cheaper vender with a longer lead time.

Things TODO:
  • The Fuse blades are just running the lights. These will be moved and run off a more proper fuse box.
  • The inverter board will be propped up with more finished dow rods. I just have the 2x4s there now.
  • Need to do a full benchmark on power, from a full 100% charge to 0% discharge.
  • Need to add cross bar to top of batt box so movement will not slide the very thin rails off. Though it is very sturdy as it is.
  • Need to do a thermal analysis at high current to see if there are any issues with parts.
  • replace acrylic with laser cut for clean finish, maybe add some RBG leds for the meme.





1735956436852.png

1735956464841.png
1735956493806.png
1735956532123.png
1735956581839.png
1735956631675.png
1735956723719.png1735956776801.png
 
What did everything inside the red perimeter cost (not counting the two main leads)?

View attachment 267664
$ 2,131.10



description: CostsCostModifier: months expected/ Quantity
Unorganized receipt (ace hw - small screws washers, and extra parts )$ (48.37)$ (48.37)
Tesla Model S Battery Module 5.2KwH$ (300.00)$ (900.00)
Cable - salvaged Tesla super changer connection headper foot$ (8.75)
Tesla BMS kit - Plug-and-Play Retrofit Kit - Rev.B$ (198.14)$ (651.63)
Project board$ (30.00)$ (30.00)
South Bend Components 150A Marine Rated Battery Fuse (MRBF) and Terminal Block Combo Pack, 58V DC Max, IP66, Ignition Protected$ (14.40)$ (47.35)
Single 4-Slot Rail, Silver, 1" High x 1" Wide, Solid, 2' Long$ (65.22)
Triple Rail, Silver, 3" High x 1" Wide, Solid, 2 Feet Long$ (69.30)
Double Rail, Silver, 1.5" High x 1" Wide, Solid, 2 Feet Long$ (63.36)
BLCCLOY 10Sets 10 Series 1" x 1" Aluminum Extrusion Profiles Corner 1010 Series Angle Bracket Connector with T Slot Nuts Bolts for 1 Inch x 1 Inch Extruded Aluminium Profile Rail$ (89.89)
Misc mounting parts$ (9.80)
outdoor HW supply - 4AWG 3/8" wire connections 4 pack$ (38.20)
Covid office deviders (FB marketplc)$ (20.00)
M8 x10pcs, 25mm stainless Steel Hexagon Head with Serrated Flange Cap Screw Bolt Hex Washer Head$ (14.92)
M8 X 10pcs stainless Hexagon Flange Nuts$ (4.80)
Power Distribution Block M8 Screw Terminal Bus Bar DC 48V 300A for Automobile Boat R$ (16.78)
Power Distribution Block M8 Screw Terminal Bus Bar DC 48V 300A for Automobile Boat RV$ (16.56)
12V-48V 100A-300A Car Auto RV Marine Boat Single Circuit Selector Isola$ (36.15)
Grand Total
$ (2,131.10)


I would say the most notable cost savings about this batt box was that I had all tools on hand to assemble, I saved a lot on cable and the batteries because I went to a salvage yard in Sacramento and bought with cash. The acrylic dividers were waste from the covid days. The switches, bus bars and other stainless steel parts I ordered directly from china on ali and patiently waited a month for arrival rather than through amazon dropshippers.
 
Thanks.

I just loathe Tesla NCA modules. Between safety and cost, they have no legit place in power system applications anymore with the widespread availability of LFP cells. They also have poor cycle life if you use max capacity. Your ~14kWh battery pack is really only .6*14kWh = 8.4kWh usable.

A brand new 16kWh DIY LFP battery would have been cheaper.

I'm also the guy that invested nearly $7K (inc. $1k Batrium BMS) into 46.6kWh worth of Panasonic plug-in-hybrid NMC cells (588 total). It took me 2+ years to build half of the 14S battery, and I'm obviously only halfway done.

I could have gone with 48kWh worth of LFP and been done 4 years ago. :P
 
Thanks.

I just loathe Tesla NCA modules. Between safety and cost, they have no legit place in power system applications anymore with the widespread availability of LFP cells. They also have poor cycle life if you use max capacity. Your ~14kWh battery pack is really only .6*14kWh = 8.4kWh usable.

A brand new 16kWh DIY LFP battery would have been cheaper.

I'm also the guy that invested nearly $7K (inc. $1k Batrium BMS) into 46.6kWh worth of Panasonic plug-in-hybrid NMC cells (588 total). It took me 2+ years to build half of the 14S battery, and I'm obviously only halfway done.

I could have gone with 48kWh worth of LFP and been done 4 years ago. :P

Yep for sure all lessons I learned, "8.4 usable" is almost the exact number I got down to with testing not outside the overcharge and undercharge and considering voltage drop from loading effect. Using LFP was the advice given to me by a coworker after I already bought the packs, who I am pretty sure is active on this forum.

I started this LV system subproject in September. And first defined the budget based on what a contracted solution would cost :sick:, and set the upper bound at 50% of that. So that gave me a budget about 2.5k for the batt box. I ended up going with the Tesla NCA because density per foot was very important to me with it in a van and I thought only 2 batteries would already be plenty enough, or for $300 a piece I could swap the failing component (hence the original hot spare plan). but yes with the effective yield loss LFP would have actually had the same density per foot.

The other reason I went with the Tesla NCA was being new at this, I was not afraid of of burning myself or building something wrong, but rather getting screwed by vendors. paying $500 per tesla pack to have it be a fully deployable solution that I knew uses legitimate Panasonic cells, and had past a very strict QC (at least once in its life), and is an asset that's value at inception was very high.

LFP batteries scared me because they would either feel too cheap to be good buying them directly from a vendor in China with unknown QC standards, no vendor relationship, and a lot of the purchase cost going to shipping (fear the vendor cheaps out to stay competitive on price) or buy from a reputable re-seller but then pay markups, still probably hazmat shipping, and needing more parts and more labour time (as the ultimate project in this case is the van) to make it into a finished system.

Would add to my list of things I wish I did was consult this forum more when I started. But I think the Tesla NCA modules could be a value if I did not need to design the mounting around a part not meant to be used like this and used a BMS that better parallelized the modules.
 