A couple of years ago hurricane Ida ripped my breaker panels off the wall, so I had the replacements installed on the inside of the house. At the same time, we wired for a whole house generator and a future solar system. I took my best guess on wire sizes and had them all installed at the same time. The generator worked out great, and now it's time for the solar system.

I was planning to use the EG4 6000XP and ~20KWH of batteries. After re-reviewing my power needs, I realized the EG4 12000XP might be a better pick, but the wire size might not make it. We installed two runs of 4/4/4/6 aluminum SER (for AC_in and AC-out), which is rated for 65 amps (75 amp @90 degC). The 12000XP has max AC out of 50 amps. However, it's breaker is rated for 100 amp, and the installation manual says to use 3 AWG copper, minimum, which is rated for 100 amps. Can I use the 4/4/4/6 SER, or ???
 
If you are following the NEC then you are required to use the 60° column when using conductors smaller than #1, the 60° column in the table for ampacity of conductors says the #4 Aluminum is rated for 55 amps.
 
Sorry, but no.
The 100A minimum transfer abilities keep you from running that load.
Sorry.

I would pull it, and run 1/0-1 SER...ALUMINUM, OR #3 copper.
How long a run are we talking?
Is there conduit?
 
You would need 2 other breakers. AC in and out
You mean to add breakers in-line? I was kinda considering doing that anyway. I like having a convenient means of disconnect, right next to the equipment.

I would never use aluminum personally
Not my first choice either, but at the time, prices were pretty high. One run for the generator and two for solar were > $2200 in aluminum. As I recall, copper was way more. It just wasn't in the budget.

If you are following the NEC then you are required to use the 60° column when using conductors smaller than #1,
Hmm, good to know, I've never heard that. By the way, the ampacy chart I usually use doesn't have a column for 60 deg; wonder why?

How long a run are we talking?
Is there conduit?
About 75-90 ft each. No conduit, it's all in the attic. 200' of 1/1/1/3 aluminum is ~$500. 200' of 3/3/3/5 copper is ~$2000 Prices from https://nassaunationalcable.com/

You can use the existing wiring, as long as you protect it from being overloaded.
Hmm, good point. So, I can use the existing wire if I size the breakers appropriately. I think this may be the same as @SomethingAppropriate was suggesting. I was hoping I could start with this wire and maybe up-size later, after getting some experience with it.
 
You mean to add breakers in-line? I was kinda considering doing that anyway. I like having a convenient means of disconnect, right next to the equipment.


Not my first choice either, but at the time, prices were pretty high. One run for the generator and two for solar were > $2200 in aluminum. As I recall, copper was way more. It just wasn't in the budget.


Hmm, good to know, I've never heard that. By the way, the ampacy chart I usually use doesn't have a column for 60 deg; wonder why?


About 75-90 ft each. No conduit, it's all in the attic. 200' of 1/1/1/3 aluminum is ~$500. 200' of 3/3/3/5 copper is ~$2000 Prices from https://nassaunationalcable.com/


Hmm, good point. So, I can use the existing wire if I size the breakers appropriately. I think this may be the same as @SomethingAppropriate was suggesting. I was hoping I could start with this wire and maybe up-size later, after getting some experience with it.
or run a second run of the same and connect them with buss bar system. personally i do not like the idea of aluminum either.. too many trailer fires when I was younger for the folks living in trailers in my area, but thats when they first started using aluminum wires
 
If you are following the NEC then you are required to use the 60° column when using conductors smaller than #1, the 60° column in the table for ampacity of conductors says the #4 Aluminum is rated for 55 amps.
What code requires all sub #1 to follow the 60° column? If this is true, why would the NEC have 75° and 90° columns for sub #1 wires?
 
What code requires all sub #1 to follow the 60° column? If this is true, why would the NEC have 75° and 90° columns for sub #1 wires?
The other columns are for derating formulas, and commercial use where 75 and 90C connections are available.
If you check, the breakers are rated for a max 75C, so as long as BOTH ends you are connecting to allow 75C, you can use it at that rating.
 
The other columns are for derating formulas, and commercial use where 75 and 90C connections are available.
If you check, the breakers are rated for a max 75C, so as long as BOTH ends you are connecting to allow 75C, you can use it at that rating.
I'm familiar with the connections rating limiting the wire rating. But it has nothing to do with gauge
 
oh crud, jsut double up, spend the money and learn how to get around asinine rules... yes one set of wires will not be enough. double up and move on with the project.
 
Could I use something like a Polaris connector on each end; 2 x 4 AWG in and 1 AWG out?

I am not a code guy, but @timselectric can answer that... i just know if you double up the cables and land them on a solid copper busbar you will carry the load. Tim can tell you whats legal.... I personally know I would not give to f-s as long as my family will wake up in the AM.
 