A couple of years ago hurricane Ida ripped my breaker panels off the wall, so I had the replacements installed on the inside of the house. At the same time, we wired for a whole house generator and a future solar system. I took my best guess on wire sizes and had them all installed at the same time. The generator worked out great, and now it's time for the solar system.
I was planning to use the EG4 6000XP and ~20KWH of batteries. After re-reviewing my power needs, I realized the EG4 12000XP might be a better pick, but the wire size might not make it. We installed two runs of 4/4/4/6 aluminum SER (for AC_in and AC-out), which is rated for 65 amps (75 amp @90 degC). The 12000XP has max AC out of 50 amps. However, it's breaker is rated for 100 amp, and the installation manual says to use 3 AWG copper, minimum, which is rated for 100 amps. Can I use the 4/4/4/6 SER, or ???
I was planning to use the EG4 6000XP and ~20KWH of batteries. After re-reviewing my power needs, I realized the EG4 12000XP might be a better pick, but the wire size might not make it. We installed two runs of 4/4/4/6 aluminum SER (for AC_in and AC-out), which is rated for 65 amps (75 amp @90 degC). The 12000XP has max AC out of 50 amps. However, it's breaker is rated for 100 amp, and the installation manual says to use 3 AWG copper, minimum, which is rated for 100 amps. Can I use the 4/4/4/6 SER, or ???