Here is what I am trying to accomplish with this thread: Properly replace my existing battery bank with a matched set of LifePo4 batteries; with those batteries connected to each other and to my existing system for a closed-loop communications system resulting in increased efficiency and stability.
I am hoping to get feedback from folks as to what I am thinking for the new configuration, cabling, etc. All thoughts, issues, concerns, and/or questions will be appreciated. I am sincerely hoping to get it right the first time.
Existing system:

Why Powerflo5 batteries? 1) great reviews and great name recognition, 2) got a killer deal from a local supplier, 3) have used MidNite products for years with zero failures or problems.
Proposed battery configuration:
Second question: #2awg terminals are included in the box with the battery. I thought it might be a mistake...until I started doing some math and research. The batteries are 75a nominal and 100a maximum charge/discharge. Considering my cable runs are <5’, that means #4awg is sufficient, #2awg is a nice safety margin. Each battery has a built-in BMS shut down at 100a, plus a 125a circuit breaker. And if I am reading the charts right, a 125a breaker will protect a <5’ run of #2awg just fine. Even with 2 batteries in a bank it appears that #2awg will be just fine. So each battery in a bank will be connected to each other via #2awg, and the bank will be connected to the busbar via #2awg as well. Any thoughts?
Third question: Since each battery has a circuit breaker, it also acts to isolate the battery from the busbar. And turning off both batteries isolates that bank from the busbar. That means no need for a battery switch for either a battery or the bank. Agree or thoughts?
Fourth question: Since each battery has a circuit breaker there is no need for any fusing between the battery and the busbar or between batteries. Agreed or thoughts?
Fifth question: Even with 4 ‘banks’ I plan on daisy-chaining all 8 batteries via the comm ports. The Pylontech BMS software will ID the master which will be hooked to the CC-GX “ve.can” port. Even though there are technically 4 banks, each battery will still be communicating properly with the master if I am thinking it through correctly. Any thoughts or potential problems with this?
Sixth question: Since I will be connecting the ‘master’ battery to the CC-GX ve.can port (after removing the Victron Shunt cable from the CC-GX) and enabling BMS control (which automatically enables DVCC) there is no longer a need at all for the Victron Shunt. Agreed or thoughts?
Seventh question: Since the CC-GX is an earlier, and more primitive version, of the Cerbo GX, does anyone see problem using the CC-GX vs the Cerbo GX? They both use the “ve.can” ports and both support DVCC.
Open forum: I would sincerely appreciate any additional thoughts, potential issues, possible problems, or any questions from folks regarding this upcoming change. Please feel free to join in!
I am hoping to get feedback from folks as to what I am thinking for the new configuration, cabling, etc. All thoughts, issues, concerns, and/or questions will be appreciated. I am sincerely hoping to get it right the first time.
Existing system:
- 100% off-grid
- 5.5kw of PVs
- 10kw of inverter power
- 32.7kwh of LifePo4 batteries
- Canadian Solar PV’s (primarily, 4.7kw out of the 5.5kw)
- 2 x 150/70 Victron MPPTs (master/slave configuration, connected to GX via “ve.direct) port
- 2 x Victron Quattro 5K/120v/70a (split-phase configuration, comms daisy chained connected to GX via “ve.bus” port)
- Color Control GX “brain”
- Victron Lynx Shunt connected to the GX “ve.can” port
- 2x205ah LifePo Elite batteries + 1x 230ah LifePo Trophy battery (none of the batteries are comm connected to each other and not connected to the GX)
- I am using a 1000a Victron PowerIn as my busbar for the batteries.
- Each battery is currently wired to the busbar with a battery switch to isolate the battery from the busbar. I am using 2/0 for each battery, 4/0 busbar to shunt.
- I have a 400a Class T fuse between the busbar and the Victron Shunt.
- 8 x Midnite Solar Powerflo5 batteries (replacing all existing batteries)

Why Powerflo5 batteries? 1) great reviews and great name recognition, 2) got a killer deal from a local supplier, 3) have used MidNite products for years with zero failures or problems.
Proposed battery configuration:
- 4 ‘banks’ of batteries paralleled to 1000a busbar (Victron PowerIn)
- each ‘bank’ will be 2 batteries wired in parallel
Second question: #2awg terminals are included in the box with the battery. I thought it might be a mistake...until I started doing some math and research. The batteries are 75a nominal and 100a maximum charge/discharge. Considering my cable runs are <5’, that means #4awg is sufficient, #2awg is a nice safety margin. Each battery has a built-in BMS shut down at 100a, plus a 125a circuit breaker. And if I am reading the charts right, a 125a breaker will protect a <5’ run of #2awg just fine. Even with 2 batteries in a bank it appears that #2awg will be just fine. So each battery in a bank will be connected to each other via #2awg, and the bank will be connected to the busbar via #2awg as well. Any thoughts?
Third question: Since each battery has a circuit breaker, it also acts to isolate the battery from the busbar. And turning off both batteries isolates that bank from the busbar. That means no need for a battery switch for either a battery or the bank. Agree or thoughts?
Fourth question: Since each battery has a circuit breaker there is no need for any fusing between the battery and the busbar or between batteries. Agreed or thoughts?
Fifth question: Even with 4 ‘banks’ I plan on daisy-chaining all 8 batteries via the comm ports. The Pylontech BMS software will ID the master which will be hooked to the CC-GX “ve.can” port. Even though there are technically 4 banks, each battery will still be communicating properly with the master if I am thinking it through correctly. Any thoughts or potential problems with this?
Sixth question: Since I will be connecting the ‘master’ battery to the CC-GX ve.can port (after removing the Victron Shunt cable from the CC-GX) and enabling BMS control (which automatically enables DVCC) there is no longer a need at all for the Victron Shunt. Agreed or thoughts?
Seventh question: Since the CC-GX is an earlier, and more primitive version, of the Cerbo GX, does anyone see problem using the CC-GX vs the Cerbo GX? They both use the “ve.can” ports and both support DVCC.
Open forum: I would sincerely appreciate any additional thoughts, potential issues, possible problems, or any questions from folks regarding this upcoming change. Please feel free to join in!