Samsonite801
Solar Wizard
- Oct 15, 2020
- 2,988
No they aren't, not providing backup for house without disconnecting from grid.
Sol-Arc has AC in, AC out, transfer time 4ms.
That's just a relay inside, works like a transfer switch. Only the downstream loads are protected, like any other UPS.
50A limit on pass-through current.
If you have V2H, it can't just be a cable plugged into the house wiring.
It needs a disconnect switch to isolate grid.
When using a generator you need a transfer switch (DPDT) to move both hot legs from grid to generator.
A UPS like Sol-Arc has DPST because it's inverter section can backfeed the grid, UL1741.
Your V2H solution would have a switch to disconnect from grid, and a signal to vehicle telling it to send AC to house. Could be a vehicle charger with battery inverter, getting its DC from vehicle.
An ideal implementation would communicate with household loads and GT inverters, managing them.
Couldn't a V2H connection just plug into the generator input of a Sol-Ark and let the Sol-Ark manage it as an eligible input source, regardless of whether the AC grid input is providing power or not?