Hi gang,
I recently installed an off-grid system, with 3000W PV array, MPPT 60 150, SW-4048 and a 48V battery bank made of 8 S6-460AGM batteries. Everything is hooked up, batteries are charging on solar and inverter is inverting.
I am looking at some expertise to review the charging graphs attached and have some feedback. I have contacted Rolls customer support who gave me the following parameters:
Inverter Settings Must be set to Custom.
Equalization support: current = "disabled"
Equalization voltage: 58.8V
Bulk voltage: 58.8V
Bulk Termination voltage: 58.8V?
Absorb voltage: 58.8V
Float voltage: 55.2V
Battery temp comp: 96mV/C
They said that low battery cut out and high battery cut out were a personal choice, even though I specifically asked for a 50% depth of discharge... I setup LBCO = 49V and HBCO = 59.5V. When the sun kicked in today, the inverter threw an error stating that it hit the high battery cut out. I raised the HBCO to 62V and cleared the error. Please see below for the graphs of the day (not sure what happened between 2pm and 4pm...)
They also told me to use the manual to calculate my absorption time, which I did:
- with CC at ~40 amp: 0.38x415/40 = 240 minutes
- with inverter at ~30 amp: 0.38x415/30 = 315 minutes.
I also contacted Schneider support but they have not been much help so far...
Anyone having a similar setup? Any feedback appreciated, thanks!
P.S: I'll post a updated pic of the charge graph tomorrow.
I recently installed an off-grid system, with 3000W PV array, MPPT 60 150, SW-4048 and a 48V battery bank made of 8 S6-460AGM batteries. Everything is hooked up, batteries are charging on solar and inverter is inverting.
I am looking at some expertise to review the charging graphs attached and have some feedback. I have contacted Rolls customer support who gave me the following parameters:
Inverter Settings Must be set to Custom.
Equalization support: current = "disabled"
Equalization voltage: 58.8V
Bulk voltage: 58.8V
Bulk Termination voltage: 58.8V?
Absorb voltage: 58.8V
Float voltage: 55.2V
Battery temp comp: 96mV/C
They said that low battery cut out and high battery cut out were a personal choice, even though I specifically asked for a 50% depth of discharge... I setup LBCO = 49V and HBCO = 59.5V. When the sun kicked in today, the inverter threw an error stating that it hit the high battery cut out. I raised the HBCO to 62V and cleared the error. Please see below for the graphs of the day (not sure what happened between 2pm and 4pm...)
They also told me to use the manual to calculate my absorption time, which I did:
- with CC at ~40 amp: 0.38x415/40 = 240 minutes
- with inverter at ~30 amp: 0.38x415/30 = 315 minutes.
I also contacted Schneider support but they have not been much help so far...
Anyone having a similar setup? Any feedback appreciated, thanks!