Has anyone tried one of these SSRs with an Orion BMS? I'd love to be able to use one of these without a separate relay.
I am using 4 DCC-300A (version 1.0, first issue) with Royal Excelene 4/0 cable (83mm) with Selterm Tinned Lugs (5/16 hole).I have a concern about the lug sizes on the DCC's, for example the Victron multiplus 48/5000 I intend to use the DCC/Chargery with, requires 1x set of 70mm cables up to 5m and 2x sets of 70mm for 5-10m.
Working on the recommended fuse sizes and current calculations, i.e 9000w surge/48v = 187A.
I could use a 200A DCC, however the cable size requirements (70mm lugs) will not fit on the 200A.
Are the lug sizes in the DCC info 50-8 in this case the maximum size lugs that fit?
I've seen many systems have trouble with low AC output under load due to poor DC wiring sizes.
EDIT: looking at the DCC manual and the cabac lug sizes, it looks like 70-8 lugs will fit the 300. Just
I am using 4 DCC-300A (version 1.0, first issue) with Royal Excelene 4/0 cable (83mm) with Selterm Tinned Lugs (5/16 hole).
In my case I had to modify the lugs because the first version of the DCC had shorter terminals.
TWO Methods to Install the DCC as well.
Option One: Install it on the NEG side, after the shunt. BATT to Shunt to DCC to Inverter/Load/Charger.
Option Two: Install it on the POS side, with the ISO Board installed between the BMS & DCC. Setup would be BATT to DCC to Inverter/Load/Charger.
I've pulled 250A @ 24V Draw through a single DCC without any issues, not even triggering the cooling fan. I've pushed just a bit over 150A Charge through a single DCC and again without any issue whatsoever.
Steve,I just got a package from Jason which included the new External Power Adapters for the BMS', installed them this morning and the voltage readings and such have really settled down nicely. It is making a difference in the internal passive balancing as well as it reads values more sensibly. At present I am pushing 135A charge into the bank and eagle eyeing it.
I was also sent the ISO Board adapter to put between the DCC & BMS for (+) line Operation. I have not installed those at this time as I am wired to use the DCC on the NEG line per the original instructions as provided by Jason. I may test this when I assemble the next pack to go into place, as my LFP bank is production, so I can't / won't futz much with it. Ain't broke don't fix it. It also means cutting up more of my 4/0 cabling and crimping on more lugs and to be honest, I've had to spend Far More on wire than I ever intended to with all the changes.
@Cal, if you want, I can do some quicky tests with a DMM if you specify what exactly you'd like to see... step-by-step instructions. The current charge run on the bank will run another 3.5-4.0 hours yet.... I bottomed the whole bank to just tickling 0% SOC on all packs, prior to this charge run. Once this part is done (the LFP's), I'll be running a Deep Charge on my FLA Bank for 4 hours, so the day is accounted for.
BTW: Using BMS8T-300's with 1st issue 300A DCC's on the Negative Line after the Shunt. (Batt to Shunt to DCC to Common DC Busbar and out)
.
I'm still configured on the Negative Side for the DCC. Installed the ISO Board & the external power board interface and the BMS' are quite settled and certainly behaving better overall, much less "jumpy" as was way back when.Steve,
I've not been so active on here lately just so busy and maybe missed somewhere you've mentioned on the modification to the first DCC's of the short terminal's. Hoping to get some 3D prints finished and start putting everything together on my project and wasn't sure about this. But seems I've missed out on few other options here that I might need to look into. Now we can use it on positive (advantage being?) also we have a board with diode to run into the external power side of the BMS. This would be all great to consider in the installation.
My apologies I did not go to the end of this post to see you have already answered to my last question.I prefer to have a "Margin" on all things, cannot be having a failure when it is -35C or +40C outside (that is normal for here).
because of my wires & lugs, I had to trim the Lugs a little for clearance BUT see below.
See this post for more info. (First Issue V1.0 though)
Chargery BMS, DCC (Solid State Contactor) thread.
Good Day folks, I am starting this thread related to the Chargery DCC, so the first post will be a basic "intro". See the following posts for more info. The DC contactor is designed specially to work with the CHARGERY BMS', the following are some features: Bi-directional connection, one...diysolarforum.com
For me I think I'm skipping the ISO board this is just something extra in the setup I dont need. Want to keep it simple and have hard time making room for it all as it is.I'm still configured on the Negative Side for the DCC. Installed the ISO Board & the external power board interface and the BMS' are quite settled and certainly behaving better overall, much less "jumpy" as was way back when.
I'm not sure how Jason is dealing with that and the new "P" models. I'm assuming it's all incorporated internally. I'd hope so.
This is exactly the kind of thing I was hoping to see and is convincing me I should abandon the ‘simple’ all-in-one BMS architecture for the Chargery approach with separate DCC (building an 8S LiFePO4 for 2-4KW of off-grid solar).I am using 4 DCC-300A (version 1.0, first issue) with Royal Excelene 4/0 cable (83mm) with Selterm Tinned Lugs (5/16 hole).
In my case I had to modify the lugs because the first version of the DCC had shorter terminals.
TWO Methods to Install the DCC as well.
Option One: Install it on the NEG side, after the shunt. BATT to Shunt to DCC to Inverter/Load/Charger.
Option Two: Install it on the POS side, with the ISO Board installed between the BMS & DCC. Setup would be BATT to DCC to Inverter/Load/Charger.
I've pulled 250A @ 24V Draw through a single DCC without any issues, not even triggering the cooling fan. I've pushed just a bit over 150A Charge through a single DCC and again without any issue whatsoever.
Thanks, I’ll start looking into the BMS8T.DCC lugs are already sorted.... I got first set out.
I am using a BMS8T which is for 8S and lower.
The New BMS * "P" and others are supposed to be out by end of month as far as I know.
Very nice design and a good reference for what I am trying to put together (on a smaller scale).One fuse per Battery on the + side obviously.
The BMS8P, BMS16P & BMS24P are the New BMS' coming out with Active Balancing and the "goodies" we've asked for.
DCC's have already been revised, but possibly more will be done for them too... I DUNNO
Myself, I have an MRBF Fuse on each battery pack, on the (+) terminal
From "About My System" pages:
The LFP BANK: (photo, before ISO Board & External Power feed to BMS' were installed.)