Had a few issues today, and just looking for a sanity check on what I experienced and observed and identified as issues.
I was charging my system from zero percent SoC today, and the Class T fuse started to smoke! I could feel the heat coming from the holder and the wire on the battery side of the fuse. At the time the Cerbo GX was reporting 90 amps flowing into the system - this was a first for me. The battery has never been this low and never had 90 amps going into it - but I believe it should handle that just fine.
This is a marine installation, and I've built a 12v 304aH battery from 4 Eve cells (LF304). BMS is Rec-BMS and charger is Victron Multi-Plus Compact inverter / charger. There is a CerboGX providing the brains to the system. I've been away from the boat for 4 months, and through some shore power outages and unintended power usage and configurations, the battery found itself 'dead' - I think it was around 8.5V - it's been this way for about 4 weeks.
My understanding is when Shore Power returned, the MultiPlus doesn't power up and charge because it's waiting for a message from the Cerbo - but the 12v side of the system is so dead, the Cerbo is offline and therefore the system can never turn on. Is that correct? I read that you could disconnect the network cable and it should work. I disconnected from the Cerbo and there was no change. I didn't try disconnecting from the MultiPlus as that requires opening it up.
I got a 12v trickle charger powered from Shore to help feed the system. It's a 6 amp charger. Knowing I could be here a long time, I also flipped my DC to DC charger that charges the engine starter battery to use it to help charge the lithium bank. After not too long there was enough volts to boot up the Cerbo, however the BMS didn't want to come online (maybe not enough volts), My understanding is the Cerbo wouldn't tell the MultiPlus to charge because it couldn't talk tot he BMS and be sure it was 'allowed' to charge. Is that correct?
I turned off DVCC to get over this restriction an and rebooted the system. Once back up, the charger went full steam ahead and was charging at 90amps. With enough voltage coming in the BMS was now online as well. After 5 minutes or so I could smell some electrical burning. Upon investigation I could see some discolouration of the Class T fuse. It's a 300 Amp Busman - sold by the local chandlery (https://www.eaton.com/content/dam/e...circuit-fuses/class-t/bus-ele-ds-1025-jjn.pdf), installed into a BlueSea Holder. I moved a temperature sensor closer to motor the temperature, and as I went back to my computer to see readings, I noticed some light smoke from the fuse. At this point I quickly stopped the charger system. I turned DVCC back on and rebooted again. After reboot the system went back to charging at 30amps (as restricted by the BMS - I've never changed this setting up until now).
So I'm looking for a sanity check that everything is sized properly. A 0.5 Charge or Discharge on the cells would be 150 amps. We we only at 90, so I think I'm ok here. The wiring from the battery to the fuse block is 2/0 gauge - Also ok?. The same size going from the MultiPlus through a Lynx Distribution. The only point of heat seemed to be on the battery side of the Class T Fuse.
I had done a bit of a push and pull on on the fuse and wire connections and nothing was lose. However, when I pulled off the fuse I noticed a few things:
- Discolouration of the mounting bolt for the battery side of the fuse.
Upon removing the fuse, I noticed the other side of the fuse was not tight at all, the nut could be hand removed. Behind this there was some white on the fuse holder:

If the connection on the left side was poor, would I expect to see over heating on the right side? I think this makes sense.
The BMS has previously been set to limit charging at 30amps, from factory settings. I'm about to replace the alternator on the boat engine with a 90Amp Balmar in order to charge this battery faster, so I'm just looking for reassurance that this is setup and sized properly, and this all comes down to a loose nut!
Thanks for hanging in and reading to the end!
I was charging my system from zero percent SoC today, and the Class T fuse started to smoke! I could feel the heat coming from the holder and the wire on the battery side of the fuse. At the time the Cerbo GX was reporting 90 amps flowing into the system - this was a first for me. The battery has never been this low and never had 90 amps going into it - but I believe it should handle that just fine.
This is a marine installation, and I've built a 12v 304aH battery from 4 Eve cells (LF304). BMS is Rec-BMS and charger is Victron Multi-Plus Compact inverter / charger. There is a CerboGX providing the brains to the system. I've been away from the boat for 4 months, and through some shore power outages and unintended power usage and configurations, the battery found itself 'dead' - I think it was around 8.5V - it's been this way for about 4 weeks.
My understanding is when Shore Power returned, the MultiPlus doesn't power up and charge because it's waiting for a message from the Cerbo - but the 12v side of the system is so dead, the Cerbo is offline and therefore the system can never turn on. Is that correct? I read that you could disconnect the network cable and it should work. I disconnected from the Cerbo and there was no change. I didn't try disconnecting from the MultiPlus as that requires opening it up.
I got a 12v trickle charger powered from Shore to help feed the system. It's a 6 amp charger. Knowing I could be here a long time, I also flipped my DC to DC charger that charges the engine starter battery to use it to help charge the lithium bank. After not too long there was enough volts to boot up the Cerbo, however the BMS didn't want to come online (maybe not enough volts), My understanding is the Cerbo wouldn't tell the MultiPlus to charge because it couldn't talk tot he BMS and be sure it was 'allowed' to charge. Is that correct?
I turned off DVCC to get over this restriction an and rebooted the system. Once back up, the charger went full steam ahead and was charging at 90amps. With enough voltage coming in the BMS was now online as well. After 5 minutes or so I could smell some electrical burning. Upon investigation I could see some discolouration of the Class T fuse. It's a 300 Amp Busman - sold by the local chandlery (https://www.eaton.com/content/dam/e...circuit-fuses/class-t/bus-ele-ds-1025-jjn.pdf), installed into a BlueSea Holder. I moved a temperature sensor closer to motor the temperature, and as I went back to my computer to see readings, I noticed some light smoke from the fuse. At this point I quickly stopped the charger system. I turned DVCC back on and rebooted again. After reboot the system went back to charging at 30amps (as restricted by the BMS - I've never changed this setting up until now).
So I'm looking for a sanity check that everything is sized properly. A 0.5 Charge or Discharge on the cells would be 150 amps. We we only at 90, so I think I'm ok here. The wiring from the battery to the fuse block is 2/0 gauge - Also ok?. The same size going from the MultiPlus through a Lynx Distribution. The only point of heat seemed to be on the battery side of the Class T Fuse.
I had done a bit of a push and pull on on the fuse and wire connections and nothing was lose. However, when I pulled off the fuse I noticed a few things:
- Discolouration of the mounting bolt for the battery side of the fuse.
Upon removing the fuse, I noticed the other side of the fuse was not tight at all, the nut could be hand removed. Behind this there was some white on the fuse holder:

If the connection on the left side was poor, would I expect to see over heating on the right side? I think this makes sense.
The BMS has previously been set to limit charging at 30amps, from factory settings. I'm about to replace the alternator on the boat engine with a 90Amp Balmar in order to charge this battery faster, so I'm just looking for reassurance that this is setup and sized properly, and this all comes down to a loose nut!
Thanks for hanging in and reading to the end!