I am building a system with two MPPT 100/600s feeding a single XW Pro 6848 with a mini-PDP.
I would like to mount both CCs on the right side of the 6840 and mini-PDP combination. What is the most safe (and elegant) method of running the wiring from the PDP across the first CC to the second? I see pics of them ganged up but no details.
It looks as if the CCs are intended to have 48 V DC exit on the left and 600V DC come in from the right. But you can't do that when two are attached. I see the lexan divider. Do you run 48 V on top and 600V at the bottom and bend the lexan to form a upper and lower wireway?? My battery wire is UL 600V but I don't like mixing lethal and non-lethal voltages.
I have seen one installation where they made a hole in the bottom air vent - not to code. I could just space them 6 inches apart and run conduit but that takes so much space.
Any best practices?
I would like to mount both CCs on the right side of the 6840 and mini-PDP combination. What is the most safe (and elegant) method of running the wiring from the PDP across the first CC to the second? I see pics of them ganged up but no details.
It looks as if the CCs are intended to have 48 V DC exit on the left and 600V DC come in from the right. But you can't do that when two are attached. I see the lexan divider. Do you run 48 V on top and 600V at the bottom and bend the lexan to form a upper and lower wireway?? My battery wire is UL 600V but I don't like mixing lethal and non-lethal voltages.