The Schneider ac couple doc says -
The XW Pro can be connected in various configurations from just a single unit to multiple units in parallel, or in a three-phase configuration. Regardless of the system configuration however, the maximum continuous allowable rating of AC-coupled PV inverter(s) is the lesser of:
125% of maximum allowable charge power of the battery (calculated as rated continuous charge current times rated charge voltage).
125% of continuous rating of XW Pro inverter(s).
I am not understanding what this limit is for ? AC1 grid connections would be well higher than this .... The unit will frequency shift to reduce ac coupled output when needed .... I must be missing something simple.
I was hoping to use 1 inverter that would provide adequate power overnight or in a grid failure by placing all the high draw non-essentials on a subpanel that the PV inverters feed and thru to the XWPro @ 50amp breaker ( or try a new lumin panel to be selective ) The idea was no sun = no "luxury" items. Sun charge the batts , run everything. I don't really see how/why I need 2 XW's to meet the above.
I have 560Ah 48V LiFePo4 planning to run at 60-70 DoD 1C max and 0.5c recommended in/out , my AC PV supply is 16.4K Best possible case ...
The XW Pro can be connected in various configurations from just a single unit to multiple units in parallel, or in a three-phase configuration. Regardless of the system configuration however, the maximum continuous allowable rating of AC-coupled PV inverter(s) is the lesser of:
125% of maximum allowable charge power of the battery (calculated as rated continuous charge current times rated charge voltage).
125% of continuous rating of XW Pro inverter(s).
I am not understanding what this limit is for ? AC1 grid connections would be well higher than this .... The unit will frequency shift to reduce ac coupled output when needed .... I must be missing something simple.
I was hoping to use 1 inverter that would provide adequate power overnight or in a grid failure by placing all the high draw non-essentials on a subpanel that the PV inverters feed and thru to the XWPro @ 50amp breaker ( or try a new lumin panel to be selective ) The idea was no sun = no "luxury" items. Sun charge the batts , run everything. I don't really see how/why I need 2 XW's to meet the above.
I have 560Ah 48V LiFePo4 planning to run at 60-70 DoD 1C max and 0.5c recommended in/out , my AC PV supply is 16.4K Best possible case ...