I am about to do the trenching to bury all my cables, so need to get this straight
I read @FilterGuy white paper on grounding for arrays (pt3) and am still confused.
my setup is as follows
2 ground mount offgrid arrays 6kw each using ironridge racks,weebs, on top of 3" metal piping, 2 strings per array at about 17amps each string
my main service panel is 200amp bonded and with ground rod
closer to the arrays is a 125amp sub panel. connected to main panel with 3 wire (met code 15 years ago I believe)
since there was no ground wire connection from main to sub, I added a ground rod at the sub. I dont remember if I also bonded the sub, will have to check
the sub panel is also the AC input for my dual lv6548 inverters
I have the wire to run the fourth wire/ground from main to sub if needed
so my questions are...
should I run the 4th wire between main and sub ?
if I run the 4th wire, should I remove the ground rod connection at sub, and also verify sub is not bonded ?
do I need to run bare copper between arrays and sub panel ?, if so can both arrays share the wire ?
here is the portion on the white paper that Im confused by...
When there are ground mount panels pretty much all the NEC rules are the same.
- The panel frames must be connected back to the house grounding system.
- Approved grounding connections to the panel frames must be used
- Etc.
Where things get a little ‘interesting’ is whether there should be a grounding electrode at the panels.
The NEC does not require it, but many people still do it.
My preference is to not use a grounding electrode at the panels, but isolation from earth ground can be difficult to realistically achieve. - If the mounting rack is metal, there will be some amount of grounding even if there are no dedicated grounding electrodes. - Even with a wood mounting rack, when it is wet there will be some amount of grounding. However, I like to tie the required ground to the house system as close to the grounding electrode as possible. In the diagram above, it is tied into the house main breaker panel. Even better would be directly to the grounding electrodes. This will keep any pulse coming down the line away from the rest of the electrical system.
I read @FilterGuy white paper on grounding for arrays (pt3) and am still confused.
my setup is as follows
2 ground mount offgrid arrays 6kw each using ironridge racks,weebs, on top of 3" metal piping, 2 strings per array at about 17amps each string
my main service panel is 200amp bonded and with ground rod
closer to the arrays is a 125amp sub panel. connected to main panel with 3 wire (met code 15 years ago I believe)
since there was no ground wire connection from main to sub, I added a ground rod at the sub. I dont remember if I also bonded the sub, will have to check
the sub panel is also the AC input for my dual lv6548 inverters
I have the wire to run the fourth wire/ground from main to sub if needed
so my questions are...
should I run the 4th wire between main and sub ?
if I run the 4th wire, should I remove the ground rod connection at sub, and also verify sub is not bonded ?
do I need to run bare copper between arrays and sub panel ?, if so can both arrays share the wire ?
here is the portion on the white paper that Im confused by...
When there are ground mount panels pretty much all the NEC rules are the same.
- The panel frames must be connected back to the house grounding system.
- Approved grounding connections to the panel frames must be used
- Etc.
Where things get a little ‘interesting’ is whether there should be a grounding electrode at the panels.
The NEC does not require it, but many people still do it.
My preference is to not use a grounding electrode at the panels, but isolation from earth ground can be difficult to realistically achieve. - If the mounting rack is metal, there will be some amount of grounding even if there are no dedicated grounding electrodes. - Even with a wood mounting rack, when it is wet there will be some amount of grounding. However, I like to tie the required ground to the house system as close to the grounding electrode as possible. In the diagram above, it is tied into the house main breaker panel. Even better would be directly to the grounding electrodes. This will keep any pulse coming down the line away from the rest of the electrical system.