Connecting Daly BMS (BMS-GD230-309E) to Victron Cerbo GX via Daly Interface Board – Help!!!

Andreg97

New Member
Joined
Dec 1, 2024
Messages
1
Location
Italy
Good day,

I have four Daly BMS (model: BMS-GD230-309E) and would like to connect them to a Victron Cerbo GX using a Daly Interface Board. I purchased the Interface Boards specifically for Victron devices, so the appropriate firmware should already be installed.

When I connect the Interface Board to the Cerbo GX using a custom-made CAN cable, I can see that data packets are being transmitted, as indicated by the RX and TX on the can port. However, the BMS is not displayed in the Victron system.

My Daly BMS units do not have a "CAN/RS485" port on the side, only a "LED" label. The firmware version of the BMS is 32_240_515_001T.

My question is whether it is generally possible to establish a connection between my components, and what firmware or additional components might be required to get the communication working.

Thank you in advance for your support!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein „CAN/RS485“-Anschluss, sondern lediglich die Beschriftung „LED“. Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André
 
I can tell you with certainty that the Cerbo does not explicitly support DALY unless there is a custom driver available OR the BMS simulates an existing battery like Pylontech.

If you enabled DVCC on the Cerbo, you might see it.

If DVCC doesn't work, the only way I know how to connect a DALY is through a UART to USB adapter and the dbus-serialbattery driver on github.
 
Goede dag

Ik heb vier Daly BMS (model: BMS-GD230-309E) en wil deze graag aansluiten op een Victron Cerbo GX met behulp van een Daly Interface Board. Ik heb de interfacekaarten speciaal voor Victron-apparaten gekocht, dus de juiste firmware zou al geïnstalleerd moeten zijn.

Wanneer ik de interfacekaart met een op maat gemaakte CAN-kabel op de Cerbo GX aansluit, kan ik zien dat er datapakketten worden verzonden, zoals aangegeven door de RX en TX op de can-poort. Het BMS wordt echter niet weergegeven in het Victron-systeem.

Mijn Daly BMS-units hebben geen "CAN/RS485"-poort aan de zijkant, alleen een "LED"-label. De firmwareversie van het BMS is 32_240_515_001T.

Mijn vraag is of het over het algemeen mogelijk is om een verbinding tussen mijn componenten tot stand te brengen, en welke firmware of extra componenten nodig zijn om de communicatie te laten werken.

Alvast bedankt voor uw steun!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein "CAN/RS485"-Anschluss, sondern lediglich die Beschriftung "LED". Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André
 
Good day,

I have four Daly BMS (model: BMS-GD230-309E) and would like to connect them to a Victron Cerbo GX using a Daly Interface Board. I purchased the Interface Boards specifically for Victron devices, so the appropriate firmware should already be installed.

When I connect the Interface Board to the Cerbo GX using a custom-made CAN cable, I can see that data packets are being transmitted, as indicated by the RX and TX on the can port. However, the BMS is not displayed in the Victron system.

Mijn Daly BMS-units hebben geen "CAN/RS485"-poort aan de zijkant, alleen een "LED"-label. De firmwareversie van het BMS is 32_240_515_001T.

Mijn vraag is of het over het algemeen mogelijk is om een verbinding tussen mijn componenten tot stand te brengen, en welke firmware of extra componenten nodig zijn om de communicatie te laten werken.

Alvast bedankt voor uw steun!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein "CAN/RS485"-Anschluss, sondern lediglich die Beschriftung "LED". Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André
 
Good day,

I have four Daly BMS (model: BMS-GD230-309E) and would like to connect them to a Victron Cerbo GX using a Daly Interface Board. I purchased the Interface Boards specifically for Victron devices, so the appropriate firmware should already be installed.

When I connect the Interface Board to the Cerbo GX using a custom-made CAN cable, I can see that data packets are being transmitted, as indicated by the RX and TX on the can port. However, the BMS is not displayed in the Victron system.

Mijn Daly BMS-units hebben geen "CAN/RS485"-poort aan de zijkant, alleen een "LED"-label. De firmwareversie van het BMS is 32_240_515_001T.

Mijn vraag is of het over het algemeen mogelijk is om een verbinding tussen mijn componenten tot stand te brengen, en welke firmware of extra componenten nodig zijn om de communicatie te laten werken.

Alvast bedankt voor uw steun!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein "CAN/RS485"-Anschluss, sondern lediglich die Beschriftung "LED". Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André
 
Good day,

I have four Daly BMS (model: BMS-GD230-309E) and would like to connect them to a Victron Cerbo GX using a Daly Interface Board. I purchased the Interface Boards specifically for Victron devices, so the appropriate firmware should already be installed.

When I connect the Interface Board to the Cerbo GX using a custom-made CAN cable, I can see that data packets are being transmitted, as indicated by the RX and TX on the can port. However, the BMS is not displayed in the Victron system.

Mijn Daly BMS-units hebben geen "CAN/RS485"-poort aan de zijkant, alleen een "LED"-label. De firmwareversie van het BMS is 32_240_515_001T.

Mijn vraag is of het over het algemeen mogelijk is om een verbinding tussen mijn componenten tot stand te brengen, en welke firmware of extra componenten nodig zijn om de communicatie te laten werken.

Alvast bedankt voor uw steun!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein "CAN/RS485"-Anschluss, sondern lediglich die Beschriftung "LED". Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André
edenGaan
 
Good day,

I have four Daly BMS (model: BMS-GD230-309E) and would like to connect them to a Victron Cerbo GX using a Daly Interface Board. I purchased the Interface Boards specifically for Victron devices, so the appropriate firmware should already be installed.

When I connect the Interface Board to the Cerbo GX using a custom-made CAN cable, I can see that data packets are being transmitted, as indicated by the RX and TX on the can port. However, the BMS is not displayed in the Victron system.

My Daly BMS units do not have a "CAN/RS485" port on the side, only a "LED" label. The firmware version of the BMS is 32_240_515_001T.

My question is whether it is generally possible to establish a connection between my components, and what firmware or additional components might be required to get the communication working.

Thank you in advance for your support!


Guten Tag,

ich habe vier Daly BMS (Modell: BMS-GD230-309E) und möchte diese über ein Daly Interface Board mit einem Victron Cerbo GX verbinden. Die Interface Boards habe ich speziell für Victron-Geräte gekauft, sodass die passende Firmware bereits installiert sein sollte.

Wenn ich das Interface Board mit einem extra angefertigten CAN-Kabel am Cerbo GX anschließe, kann man bei RX- und TX des Ports sehen, dass Datenpakete hin und her geschickt werden. Leider wird das BMS jedoch nicht im Victron-System angezeigt.

An meinen Daly BMS befindet sich an der Seite kein „CAN/RS485“-Anschluss, sondern lediglich die Beschriftung „LED“. Die Firmware der BMS ist 32_240_515_001T.

Meine Frage ist nun, ob es grundsätzlich möglich ist, eine Verbindung zwischen meinen Komponenten herzustellen, und welche Firmware oder zusätzlichen Komponenten eventuell erforderlich sind, um die Kommunikation zum Laufen zu bringen.

Vielen Dank im Voraus!

André

Check to see if you have the inverter protocol set in the BMS. Below is how you could do that.

Connect to the PC software. Several ways of doing this. If you have the UART to USB cable you can plug that directly into the BMS and PC. The interface board may have come with a ethernet to USB cable. That can be plugged into one of the RS485 ports on the interface board and then to the PC. You can awaken the BMS by pressing the reset button on the interface board. The LED lights should come on if its awakened the BMS. Recommend doing this one at a time for each BMS.

You will need to connect to the Daly BMS thru the PC application and sign in as the administrator to change settings. Depending on the BMS type you purchased, the administrator password will either be 20211115 or 12345678.

The tab in the PC software you will need to go to will depend on the version software you are using. It will likely be under engineering or manufacturing. Search for the inverter brand field and change to Victron Energy.

Should be a second drop down called port type for selection of either canbus or RS485. For the pack that you will set as the master, select canbus. For the other packs which will act as slaves, select RS485. Save the setting.

----------------------------

The GX device requires that the information from the battery packs are consolidated into information for a battery bank, which communication coming from a single source. So the pack you set as a master will perform that function.

The canbus cable to the GX device will be connected to the interface board which is wired to the BMS that has been set as the master. Between all the interface boards you will need to add ethernet patch cables using the RS485 ports so they are cable to communicate.

-----------------------------

The DIP switches on the interface boards need to be set to identify the BMS address for each pack. First pack (address 0) should be off, off, off, off. Second pack (address 1) on, off, off, off. Third pack (address 2) off, on, off, off. Fourth pack (address 3) on, on, off, off. Note, I have had problems recently with address 1 not recognizing for some reason. So I just moved on to address 4 which would be off, off, on, off. Solved the problem and doesn't create any issues otherwise.

-----------------------------

You will also need to have one of the termination resistors that came with the GX device installed in the second VE.CAN port.

-----------------------------

You will need to change the protocol mode in the Cerbo GX. Click settings > Service > Canbus Profile. Select CAN-bus BMS 500 kbit/s. You may not need to reboot, I always do to be sure and then confirm the settings.

------------------------------

These are the things that I can think of that could be affecting your set up. Let me know how this works for you.

-----------------------------_

Last minute thought. It might be necessary to update the firmware on the BMS for the inverter protocol. Seen this on the older BMS models from Daly. When I build systems with these devices I usually go head and load the firmwares Daly provide me for both the BMS and WNT Interface boards so that I know they are right. If you need a copy let me know and I can reply with at least the WNT interface board firmware. Whether I have the BMS firmware would depend on which one you are using.