Well I see how one tries to save on wires by essentially sharing the neutral line of a 4 conductor wire on two circuits, instead of using 2 x 2 conductor wires. Normally, this doesn’t matter as the red and black hits are opposite in phase so the neutral cancels out, and will never be higher than 1x load of the red or black. So the neutral will never be over loaded. However, if one uses a backfeed breaker that shorts the red and black hots, then it is possible for the neutral to carry 2x the max current which will overload it as the red and black are now in phase and adds.OK now I need a drink. Have never envisioned this before. With the circuit shown, assuming both hot out-of-phases are loaded equally, there would be zero amps measured on the neutral wire?
View attachment 61506
This is not going to happen with a backfeed of only 15A as the backfeed input breaker will trip before this line overloads. But I can see how this can be an issue if the backfeed is say 30A and each of the shared breaker is pulling in their max, causing the neutral to overload as it will take 30A when it is rated for sal 15A. Not super likely to happen, but possible.