ecmb52
New Member
Hi Guys.
I purchased 2 6000XP inverters with a server rack & 6 / 5kw EG4 48V LL-S batteries. Can you help me verify 2 connections? FYI, This system will power essential circuits (refrig, chest freezer, well pump) and will be on its own panel! The rest of the house will be in the original main panel.
#1. All the batteries are connected in parallel. IE, all of + are connected to the positive bus and all of the – are connected to the negative bus. For the battery connection to the inverters, I simply connect each +/- wires to the corresponding bus and then the other side to the inverter. To verify, each inverter battery wire comes from the same bus. 2 runs, one to inverter 1, and the other inverter 2.
#2 AC Grid connection. The inverter manual refers to 8AWG inputs from the grid (house panel). 8AWG is rated for 40Amps. Each inverter requires an AC input. So I need 2, 2 pole 40 amp breakers in my house panel. 1 for each inverter. Is this correct?
Any input is appreciated!
Will post pictures once complete.
I purchased 2 6000XP inverters with a server rack & 6 / 5kw EG4 48V LL-S batteries. Can you help me verify 2 connections? FYI, This system will power essential circuits (refrig, chest freezer, well pump) and will be on its own panel! The rest of the house will be in the original main panel.
#1. All the batteries are connected in parallel. IE, all of + are connected to the positive bus and all of the – are connected to the negative bus. For the battery connection to the inverters, I simply connect each +/- wires to the corresponding bus and then the other side to the inverter. To verify, each inverter battery wire comes from the same bus. 2 runs, one to inverter 1, and the other inverter 2.
#2 AC Grid connection. The inverter manual refers to 8AWG inputs from the grid (house panel). 8AWG is rated for 40Amps. Each inverter requires an AC input. So I need 2, 2 pole 40 amp breakers in my house panel. 1 for each inverter. Is this correct?
Any input is appreciated!
Will post pictures once complete.