Good morning, can you guys take a look at this very rough mspaint schematic of the system I’m intending to install on my cargo trailer? I have most of the parts already.
2 x 206ah SOK LiFepro4 batteries in series for 24v.
300a ANL on the positive. Battery disconnect switch on the negative (Or should I put this on the positive cable?)
2awg pure copper cables from bank.
Victron Smart Shunt after shutoff on Negative.
positive to bus bar
negative to bus bar
200a MEGA fuse on positive to 2000w 24v Giandel Inverter
Victron 150/70 MPPT Charge Controller 80a circuit breaker fuse on the 6awg to the batteries.
6 x Rich Solar 200w 12v panels 3S2P
calculated:
Max Voltage per panel at low temp: 28.6335v
Array Max Voltage: 85.9v
Amps into CC: 19.6
Amps Out CC: 58.46
63a breaker for panels. I may have gone way overboard on the breaker But each panel is internal fused right?
does this look okay? Do I need to consider anything else?
Thanks in advance. Again, sorry for the MS Paint!
2 x 206ah SOK LiFepro4 batteries in series for 24v.
300a ANL on the positive. Battery disconnect switch on the negative (Or should I put this on the positive cable?)
2awg pure copper cables from bank.
Victron Smart Shunt after shutoff on Negative.
positive to bus bar
negative to bus bar
200a MEGA fuse on positive to 2000w 24v Giandel Inverter
Victron 150/70 MPPT Charge Controller 80a circuit breaker fuse on the 6awg to the batteries.
6 x Rich Solar 200w 12v panels 3S2P
calculated:
Max Voltage per panel at low temp: 28.6335v
Array Max Voltage: 85.9v
Amps into CC: 19.6
Amps Out CC: 58.46
63a breaker for panels. I may have gone way overboard on the breaker But each panel is internal fused right?
does this look okay? Do I need to consider anything else?
Thanks in advance. Again, sorry for the MS Paint!