I was working on my off-grid solar power installation today, adding class T fuses between the batteries and the bus bar (one class T for each battery).
The batteries are server rack style.
My steps:
1) shut down each battery's built-in breaker
2) put each battery to sleep (by pushing the reset button for 3 seconds)
3) changed the AIO from mode SBU to UTI
4) turned off the 250A breaker between the AIO and battery bus
Step 3 was probably not necessary as I had 7kW of pv input and the load was around 1kW only.
At this point, I thought it would be a good idea to also shut off the pv coming in.
5) turned off the 2 breakers between the 2 pv arrays and the AIO.
breaker 1 had 3100W (about 9.4A @ 330V)
breaker 2 had 4300W (about 16A @ 270V)
Both breakers are rated 25A. Breaker 2 had a flame shooting out on the right side.. I looked at it in an angle similar to the camera that took this photo.. about 2" were visible even though I looked at it in an angle, meaning the total length was probably 2.5" at least.
I installed 2 class T fuses and decided to put things back together. Everything is working "fine" now.
Do I need to replace the breaker that had the flame? The flame lasted perhaps 0.5 seconds.
I had bought it on Amazon and when I open the order, they don't offer the 25A version right now. The link points to a 15A version.
pv input is at the top of these breakers and the load (AIO) is on the bottom.
Was there anything wrong with my shut down procedure? Should I have shut down the pv input as step (1)?
The batteries are server rack style.
My steps:
1) shut down each battery's built-in breaker
2) put each battery to sleep (by pushing the reset button for 3 seconds)
3) changed the AIO from mode SBU to UTI
4) turned off the 250A breaker between the AIO and battery bus
Step 3 was probably not necessary as I had 7kW of pv input and the load was around 1kW only.
At this point, I thought it would be a good idea to also shut off the pv coming in.
5) turned off the 2 breakers between the 2 pv arrays and the AIO.
breaker 1 had 3100W (about 9.4A @ 330V)
breaker 2 had 4300W (about 16A @ 270V)
Both breakers are rated 25A. Breaker 2 had a flame shooting out on the right side.. I looked at it in an angle similar to the camera that took this photo.. about 2" were visible even though I looked at it in an angle, meaning the total length was probably 2.5" at least.
I installed 2 class T fuses and decided to put things back together. Everything is working "fine" now.
Do I need to replace the breaker that had the flame? The flame lasted perhaps 0.5 seconds.
I had bought it on Amazon and when I open the order, they don't offer the 25A version right now. The link points to a 15A version.
pv input is at the top of these breakers and the load (AIO) is on the bottom.
Was there anything wrong with my shut down procedure? Should I have shut down the pv input as step (1)?