they are 4 poles but they loop them through both sides to increase the voltage. Many different types with same switch.That's the one I use. 4 poles, to shut down + and - of 2 strings.
they are 4 poles but they loop them through both sides to increase the voltage. Many different types with same switch.That's the one I use. 4 poles, to shut down + and - of 2 strings.
they do it on the single pair. They loop it back so it goes through 4 contacts with two wires. Increases the voltage rating.You can do that if you want. I disconnect + and - of each string.
The IMO is rated for 700 volts. I don't need to increase the rating.they do it on the single pair. They loop it back so it goes through 4 contacts with two wires. Increases the voltage rating.
I thought it was a cool idea, all good
Interesting, I use those all time and have never had those problems but if someone takes the time to make a negative review there's a dozen more that didn't.But be sure to read the reviews first.
, but which one would you buy?
That disconnect supports a max of 32A. And two strings.I spoke with SS regarding my solar panel strings for 36 panels to the Flexboss21. They said we could do 12,12 on mppt1 and 6,6 on mppt2 and recommended using two of the following disconnect. After looking at this later, I noticed this disconnect is rated for 32amps. My question is whether connecting each sting of 12 panels to the disconnect leave it in series or does it combine the amperage? If combined, the amperage would be 43.02 amps and exceed the rated amperage.
![]()
IMO DC Disconnect Rooftop Isolator Switch | 4 Pole | 2 String
The IMO DC Disconnect Rooftop Isolator Switch ensures safe disconnection of rooftop solar systems, offering reliable operation and compliance with industry standards for enhanced system safety.signaturesolar.com
Each pole is rated for 32 amps.I spoke with SS regarding my solar panel strings for 36 panels to the Flexboss21. They said we could do 12,12 on mppt1 and 6,6 on mppt2 and recommended using two of the following disconnect. After looking at this later, I noticed this disconnect is rated for 32amps. My question is whether connecting each sting of 12 panels to the disconnect leave it in series or does it combine the amperage? If combined, the amperage would be 43.02 amps and exceed the rated amperage.
![]()
IMO DC Disconnect Rooftop Isolator Switch | 4 Pole | 2 String
The IMO DC Disconnect Rooftop Isolator Switch ensures safe disconnection of rooftop solar systems, offering reliable operation and compliance with industry standards for enhanced system safety.signaturesolar.com
That disconnect supports a max of 32A. And two strings.
If you use two of the disconnects, disconnect 1 string 1 will be 12s (at Isc of 1x), string 2 will be 12s (at Isc of 1x).
Same concept for second disconnect for mppt 2 but with two 6s strings. So you should be well under the 32A limit.
Each pole is rated for 32 amps.
Proper design per the NEC (and good practice) is to select OCPDs rated at least 25% higher than the maximum expected continuous current expected in the circuitI like the Langir double pole non-polarized DC breakers. I would also put the spike protectors on it, just stuff it in a box. I can't think of a good reason not to just go ahead and use a breaker. The only problem I had was a bit of underprovisioning, my 2nd set of panels was tripping the 25A breaker in parallel, just right on the edge NMOT was 12+A with MAX at like 12.98, feeding a 25A MPPT. Each string is feeding a 15A, combined with DINKLE's to the now 32A that feeds up to the MPPT. This way I can shut off whatever I want.