I have spare class t fuses that are 80 amps I can send for testing if you need fuses
I think the NH00 fuses are also designed to not throw molten metal around. Same principal of an enclosed ceramic fuse surround with silica sand.I wish I had more time. I have all the equipment to do these tests in my lab (I've done Class T and BS88 in the past for example).
As for the BMS (I tested the JK): in many cases and faults it will be much faster to react than the fuse, but it's not the only thing I would rely on. I size my fuses based on the max current it should see in normal operation. Inverters can fail and create a dead short, but if they normally only draw 100A, a 125A fuse will do even if the cable is rated for 200A or more.
The nice thing about Class T (and BS88) is that I have yet to see them throw molten metal/plastic around.
on a dead short the BMS stopped it before the fuse triggered? that's damn impressiveI wish I had more time. I have all the equipment to do these tests in my lab (I've done Class T and BS88 in the past for example).
As for the BMS (I tested the JK): in many cases and faults it will be much faster to react than the fuse, but it's not the only thing I would rely on. I size my fuses based on the max current it should see in normal operation. Inverters can fail and create a dead short, but if they normally only draw 100A, a 125A fuse will do even if the cable is rated for 200A or more.
The nice thing about Class T (and BS88) is that I have yet to see them throw molten metal/plastic around.
It really is. I've often theorized that a BMS sees the inverter's initial inrush as the beginning of a dead short thus goes into protection mode and shuts down.on a dead short the BMS stopped it before the fuse triggered? that's damn impressive
If a BMS can trip from the surge of charging an inverters capacitors then a true short should be an easier thing to detect.It really is. I've often theorized that a BMS sees the inverter's initial inrush as the beginning of a dead short thus goes into protection mode and shuts down.
on a dead short the BMS stopped it before the fuse triggered? that's damn impressive
yea. I've seen them blow up too. I guess it depends on what the chip is busy doing. I assume the decision to react is all on the main micro controller cpu and not some dedicated oneIt really is. I've often theorized that a BMS sees the inverter's initial inrush as the beginning of a dead short thus goes into protection mode and shuts down.
That -25kA peak could be due to magnetic field collapse but I doubt it would generate real current spike that high. Most likely that field is messing with your probes or scope.
Can also use Rogowski coil as current sensor instead of shunt.
That's the point. Wire resistance acts as a current limiter to protect the fuse. Wire inductance makes it harder for the fuse to break and arc. I use 5A fuse to protect the input of my Victron 75/15 MPPT fed from 44V Tesla battery over 20 feet of 16 gauge extension cord wire. I wanted to verify that these 250Vac rated fuses would break an arc and not explode. I measured inductance again and got 4.15 uH. Slow measured rise time could be limited by 20Mhz scope BW filter or having it zoomed out to capture entire event.But it is the resistance which is keeping it from being really exciting.
Ignition projection not protectionIn the Marine market (ABYC). This would be considered an unsafe fuse failure. As the fuse let the sparks out
Many thanx for your mature scientific approach to this very important area of concern. IMHO there is way too much trivialisation of the issues involved and worse still the market is flooded by cheap devices that will clearly not save the day when needed.Introduction
Marine Rated Battery Fuses (MRBFs) are sometimes used to replace Class T fuses due to supply chain issues, ease of installation, space constraints, and cost. However, the breaking capacity of MRBF fuses is significanly lower than that of Class T fuses as shown in Figure 1.
View attachment 202479
Figure 1. Ampere Interrupting Capacity vs DC Voltage Rating
Problem
How will an MRBF fuse behave when subjected to a dead short outside of the fuse specifications?
Background
If the fuse does not quench the arc, then hot plasma could theoretically turn the fuse into a near-perfect conductor and cause a fire, instead of a near-perfect isolator that prevents fire.
In a previous experiment, an MRBF fuse was blown using an LFP battery, and a relatively small diameter wire was used, resulting in a relatively large circuit resistance, so it may not be a conservative representation of many battery installations.
Goal
The goal is to create a practical, realistic, and relatively safe near-worst-case dead short experimental setup using a relatively large capacity (Ah) battery together with large-diameter and short-length conductors that can be used to observe how MRBF fuses behave when a dead short occurs.
Experimental setup
See Figure 2 for the experimental setup.
View attachment 202470
Figure 2. Experimental setup.
Parts used:
Some of the safety aspects for this experiment:
- MRBF fuse block and MRBF fuse rated 150A (random rating choice).
- Battery: 4 x brand new Victron Smart Lithium 330Ah 12V LFP in series, 48Vnom; never charged or discharged; NO internal BMS; Battery voltage = 52.7V = 3.29Vpc (SoC unknown).
- Battery interconnects ("busbars"/ battery cables): 4/0 AWG UL-listed pure copper. Total cable length ~20" (500mm).
- Tinned copper lugs, hammer crimped on solid concrete substrate (one sample cut in half after crimping to verify quality which was good). Lugs degreased before mounting, torqued to spec.
- Dead short initiation device: 250A snowmobile winch relay (solenoid, approx 5Ω), triggered remotely with power supply set at 14Vdc.
Theory
- Backup circuit breaking methods in the order of prioritized use:
- Use extension pole tree branch cutter. This cutter was verified to cut like a knife through butter through copper cables. Once cut, the weight of the relay (black box with black tape in Figure 2) will pull down one cut end to create a gap large enough to quench the arc. Locally remove cable insulation to reduce cutting resistance.
- In case method (1) fails: Use a stand-by impact drill set to CCW rotation with socket wrench attached to disconnect interconnect bolt.
- In case methods (1) and (2) fail: Use manual cable cutter.
- Safety goggles; gloves; fire protective clothing.
- Fire extinguisher nearby especially for extinguishing burning insulation after breaking circuit.
- Second person with phone to call for help.
The initial calculated (estimated) theoretical dead short current is approx 14,000A (14kA). This is wel outside the MRBF specs as shown in Figure 1. The instantaneous theoretical dead short power is in the order of 700,000W (700kW), which roughly matches the maximum power of a Tesla Model S Plaid . Should we really do this? Just kidding - Curiosity wins .
Results
View attachment 202467
- The fuse successfully quenched the arc in the order of one video frame rate interval, in this case 30fps, so 1/30 = 0.033s. See also Figures 3 and 4.
- The fuse polycarbonate (assumption; probably not acrylic) housing back wall blew out and landed ~10 ft away. See also Figure 5.
- Sparks of molten copper blew out and landed 1-3ft away.
- The relay welded closed (this was expected) and had to be taken apart to break the contact points loose as shown in Figure 6.
Figure 3. This is what the fuse blowing looks like in close-up (most dramatic video frame).
View attachment 202489
Figure 4. Fuse blowing process.
View attachment 202484
Figure 5. The MRBF fuse after blowing. The separation occurred at the plastic weld / glue seam.
View attachment 202493
Figure 6 - Welded relay. Only the right two studs were used.
Conclusions
When operating outside of the MRBF specs, conservatively expect at least the housing to fail and molten copper and plastic debris to fly around. This experiment is anecdotal only and needs to be repeated many times to show repeatability.
Recommendations
Ideas and criticism, preferably constructive with references when making claims, are welcome.
- Repeat this experiment to evaluate repeatability.
- Vary the fuse current rating: A 300A MRBF fuse could yield different results.
- vary the battery SoC.
- Etc.
Would you mind linking to the fuse holder you used?My NH00 fuse holder is 135mm long. 160A fuse. Like class T, the fuses and holders get bigger depending on the rating of the fuse.
Since I fuse each battery and I run a 24v system 160A for each battery is plenty for me. My largest load will come via the 3kw inverter which limits me to about 125A. I can charge at up to 115A so well within the 160A fuse rating. My NH00 fuses and holders are a fraction of the cost of class T. Even if they were twice the size, I have plenty of room