Hi all,
I'm new here, and this is my first post.
I'm seeking advice about a solar system design for an off-grid cabin.
Current equipment plan is as follows:
PhonoSolar PS270P-20/U 270W panels x6, Vmpp 31.44V, Isc 9.09A
SuperSafe SBS 190F AGM 190Ah (10hr rate) batteries x4
EPever TRIRON 4215N 40A controller x2 with temp sensors
Victron MultiPlus-II Inverter Charger 24/3000/70-32
Setup plan:
Batteries setup with 2x series pairs in parallel to make 380Ah 24V bank. Will be installed close to the inverter/charger
3 panels in series to each controller (Vocmax 124.1V, Isc 9.09A). Chassis of each string grounded. Controllers will be installed close to batteries.
Breakers sized to 1.56x Isc between panels and controllers, cables sized to 1.56x Isc.
Solar fuses and cables sized to 1.25x charge current (40A) from controllers to batteries
Breaker between battery and inverter/charger
Will have a generator connected to manually start when solar generation goes down for too long
Questions:
1. Is 80A a suitable charge current from the solar controllers for a 380Ah bank? It is just above 0.2C and I expect the constant load of the fridge to be enough to keep the actual charge rate below 0.2C, which gives lots of wiggle room for adding future constant loads without dipping below 0.1C.
2. Is my sizing of the cables, breakers and fuses correct? 1.56x Isc for the cables and breakers before the controllers, and 1.25x the charge current for the solar fuse and cables from the controllers to the batteries.
3. Am I putting breakers and fuses in the right place and using them appropriately?
- Am I missing any important OCPDs?
- Should I be using fast breaking solar fuses after the charge controllers, or standard DC fuses?
- How do I size the cable and breaker between the batteries and the inverter/charger?
4. What does the 32A rating of the AC transfer switch in the MultiPlus mean? Is it to say that when running with the generator input it can handle a maximum 32A load on the 240V outlet?
5. Is it possible to underutilise the battery storage capacity of a system in a way that is harmful long term e.g only infrequently discharging the batteries to any significant degree? I'm not sure yet what our power use will be because it will depend a lot on greenhouse setups that are yet to be considered. I want to factor in the potential for significantly more constant and intermittent loads than we currently envisage from a fridge, freezer, satellite modem, router, laptop and phone and battery chargers, but want to be sure that using a fairly small fraction of the total storage capacity at least initially won't be problematic for the health of the system.
6. Can I also run a 12V circuit off the batteries? A buck converter in parallel with the inverter/charger to run some 12V sockets from. Can include a voltage sensitive relay to stop draw if the batteries drop below cut-off.
7. Would it be wise to run a BMS with a shunt, or will I get much the same use and battery information from the inverter/charger (which won't include the use from the proposed 12V circuit)?
8. If using aluminium rails to bolt-on mount the panels, is it better to ground the rail directly or to use a grounding lug on each panel chassis and connect the string to ground that way?
My head has been absolutely spinning for the last few weeks trying to figure all of this stuff out and I apologise if I've got everything totally wrong. Certainly not expecting anyone else to do all the legwork for me so if I'm way off feel free to tell me to go back to the drawing board and start over. But any advice (and certainly any reassurance) would be very greatly appreciated. And this part of the plan doesn't include the AC distribution box that will need to be installed.
Many thanks in advance,
Simon
I'm new here, and this is my first post.
I'm seeking advice about a solar system design for an off-grid cabin.
Current equipment plan is as follows:
PhonoSolar PS270P-20/U 270W panels x6, Vmpp 31.44V, Isc 9.09A
SuperSafe SBS 190F AGM 190Ah (10hr rate) batteries x4
EPever TRIRON 4215N 40A controller x2 with temp sensors
Victron MultiPlus-II Inverter Charger 24/3000/70-32
Setup plan:
Batteries setup with 2x series pairs in parallel to make 380Ah 24V bank. Will be installed close to the inverter/charger
3 panels in series to each controller (Vocmax 124.1V, Isc 9.09A). Chassis of each string grounded. Controllers will be installed close to batteries.
Breakers sized to 1.56x Isc between panels and controllers, cables sized to 1.56x Isc.
Solar fuses and cables sized to 1.25x charge current (40A) from controllers to batteries
Breaker between battery and inverter/charger
Will have a generator connected to manually start when solar generation goes down for too long
Questions:
1. Is 80A a suitable charge current from the solar controllers for a 380Ah bank? It is just above 0.2C and I expect the constant load of the fridge to be enough to keep the actual charge rate below 0.2C, which gives lots of wiggle room for adding future constant loads without dipping below 0.1C.
2. Is my sizing of the cables, breakers and fuses correct? 1.56x Isc for the cables and breakers before the controllers, and 1.25x the charge current for the solar fuse and cables from the controllers to the batteries.
3. Am I putting breakers and fuses in the right place and using them appropriately?
- Am I missing any important OCPDs?
- Should I be using fast breaking solar fuses after the charge controllers, or standard DC fuses?
- How do I size the cable and breaker between the batteries and the inverter/charger?
4. What does the 32A rating of the AC transfer switch in the MultiPlus mean? Is it to say that when running with the generator input it can handle a maximum 32A load on the 240V outlet?
5. Is it possible to underutilise the battery storage capacity of a system in a way that is harmful long term e.g only infrequently discharging the batteries to any significant degree? I'm not sure yet what our power use will be because it will depend a lot on greenhouse setups that are yet to be considered. I want to factor in the potential for significantly more constant and intermittent loads than we currently envisage from a fridge, freezer, satellite modem, router, laptop and phone and battery chargers, but want to be sure that using a fairly small fraction of the total storage capacity at least initially won't be problematic for the health of the system.
6. Can I also run a 12V circuit off the batteries? A buck converter in parallel with the inverter/charger to run some 12V sockets from. Can include a voltage sensitive relay to stop draw if the batteries drop below cut-off.
7. Would it be wise to run a BMS with a shunt, or will I get much the same use and battery information from the inverter/charger (which won't include the use from the proposed 12V circuit)?
8. If using aluminium rails to bolt-on mount the panels, is it better to ground the rail directly or to use a grounding lug on each panel chassis and connect the string to ground that way?
My head has been absolutely spinning for the last few weeks trying to figure all of this stuff out and I apologise if I've got everything totally wrong. Certainly not expecting anyone else to do all the legwork for me so if I'm way off feel free to tell me to go back to the drawing board and start over. But any advice (and certainly any reassurance) would be very greatly appreciated. And this part of the plan doesn't include the AC distribution box that will need to be installed.
Many thanks in advance,
Simon