This seems to be a very popular setup, but thus far, nobody seems to have cracked the DaVinci code of safely using a Growatt SPF 5000 ES with a SEAUTO-TX-5000 Auto-Transformer and using the AC input of the Growatt in a 'utility first' configuration. Signature Solar has posted a schematic that appears to have concerns that are not present in this design.
Below are two designs resulting from this thread. The first, #159, is a manually cold-started version that has been deployed in the field and is currently in use by @automatikdonn. The second, #216, featuring temp and current alarms as well as automatic cold-starting, is in development and has not yet been deployed.


Jan 19 2021 Update: Although risk of using two identical SolarEdge ATs (instead of one) is likely minimal (manufactured in the same facility, same processes, and no differential loads between them), there is the potential for manufacturing tolerances to induce latent 'balance current' between multiple non-isolated transformers run in parallel. If you need more balancing capacity, use a single, larger non-isolating midpoint transformer with larger gauge windings and ferrite core.
Useful links:
Design Philosophies:
- Bake some redundancy into the system.
I know the solaredge AT's aren't free, but get a couple of them. Even though you may only *need* one for loads, run two so in case one breaks you are still good to hook.Edit Jan 19, 2021: Do not use multiple ATs in your setup. See Jan 19 2021 update below. - Sleep well at night. Transformers are reliable technology, honestly they are.
- Implement failsafes - When the BOM and schematic is done, we are going to make a video to go through the whole thing in detail. I like the ELI5(explain it like I am 5) method and @automatikdonn has generously offered to do a video at that level in the near future. Here is his implementation of design #159:
- Complexity can be managed - designs below are as simple as they can be while retaining critical safety features. If you are able to produce schematics for simpler solution that covers all grounding, fault, over-temp, over-current, over/under-voltage, cold-start, and grid-forming timing issues with a non-isolated transformer - please post.
Below are two designs resulting from this thread. The first, #159, is a manually cold-started version that has been deployed in the field and is currently in use by @automatikdonn. The second, #216, featuring temp and current alarms as well as automatic cold-starting, is in development and has not yet been deployed.
Version #159 - Attended Cold-Start
- 120/240V load center capable of handling up to 30A, with a neutral safety disconnect
- 240V load center capable of handling 1->8 GW units in parallel (single phase only)
- Conditional ground/neutral bonding of the 120V load center depending on if the GW is operating on-grid or off-grid
- No autotransformer temp sensing
- NOT YET TESTED for GFI while in on-grid mode

Version #216 (WIP) Automatic Cold Start - GitHub Link Here (PRs/forks welcomed)
- Adds temp and current monitoring to autotransformer
- Uses proven StorEdge neutral bonding method to correct the suspected on-grid GFI deficiency of design #159
- Removes manual cold start pushbutton in favor of arduino-based solution

Jan 19 2021 Update: Although risk of using two identical SolarEdge ATs (instead of one) is likely minimal (manufactured in the same facility, same processes, and no differential loads between them), there is the potential for manufacturing tolerances to induce latent 'balance current' between multiple non-isolated transformers run in parallel. If you need more balancing capacity, use a single, larger non-isolating midpoint transformer with larger gauge windings and ferrite core.
Useful links:
- Signature solar's (controversial?) wiring schematic
- @FilterGuy 's stationary systems doc?
- Troubleshooting: Neutral return with grid-tie Growatt (setting #24 external bonding relay info) @ZorbatheGeek
- Generator to Growatt Inverter Neutral Bonding - Arg @Joe BoyKey
- Growatt SPF 5000 ES Wiring for 0 Export / Need help @Mark1988 @CCAT Racing
- SolarEdge Auto-Transformer W/ Sunny Island 6048
- Ben's solar and battery - running a SE autotransformer in parallel with a split phase sol-ark 12k
- NEC Article 445
- NEC Article 250.35 - Neutral Switching & Separately Derived Systems
- NEC 250.30(A)(6)(a) Grounding Electrode Conductor, Multiple Separately Derived Systems
- Mike Holt's Article 250 Study Guide
- Growatt SPF 5000 ES manual
- Watts 24/7 hybrid inverter wiring diagram
- Lost neutral failure mode