automatikdonn
Becoming Offgrid
In my particular setup, I’m not using any grid input, because it causes problems I just don’t have time to solve at the moment. The ground bond is still done in my main service panel. I use a protran/2 panel to connect from solar to circuits.How does the ground relay play into the SPF 5000 ES neutral protection discussion, if at all? The relay appears to be designed to work with their units only. I’m curious to hear how you'd integrate the Victron AT into your system…
From the manual:
“2.4. Ground Relay
In most energy systems for residential or mobile use a TT configuration is used, which means the Neutral of the AC system is grounded. This is to ensure the GFCI breaker will trip in case there is an earth failure (The connection N/PE will ensure a current will flow in the secondary circuitry which is detected by the GFCI).
As an autotransformer is also able in some systems to “create” a neutral different from the incoming neutral, a ground relay is included in the unit. This relay can be controlled by a Multi/Quattro (by disabling the internal ground relay in the inverter/charger through VE Config or Victron Connect and interconnecting the “ground relay” terminal block in Multi/Quattro and Earth terminal block in Autotransformer by Positive and Negative conductors. In some of the diagram examples in Section 2.4.1 through 2.4.3 it is mentioned when it is possible to use the ground relay.”
Of course the built in temp protection is an advantage as well…
I know a lot of people aren’t a fan of manual switches, but I think a properly sized and architected system should have very little interventions needed.
As for handling things with the victron at, I would have to look at the relay function of it. I believe it gets the proper signaling from a victron inverter so the grounding is handled appropriately. Victron makes some really nice stuff. I have a 6kw setup for my RV that is almost entirely victron.
If that unit is just looking for a NO/NC contact, you can easily get the growatts to support that function.