Yep - exactly right. If we wanted autonomous cold-start (
option 3 of #152), the neutral verification is performed by the two over/under voltage protection relays - protecting the 120/240V load panel at all times. The only thing the cold-starting potentially risks is the AT, which is
still protected by a 30A DP CB at all times. If anybody has transformer failure experience, that'd be valuable to have here for perspective.
We should keep in mind that the OP intent was to solve the David Poz problem of a trip of the 30A CB for the AT and losing a neutral due to that. I'd say
#133 does that already, and
#152 is possibly overkill. However, we
don't monitor AT temp, which is
something SolarEdge does do (#145), so maybe
#152 isn't a bad idea, just-to-be-safe.
My personal opinion is that - if
@automatikdonn can test the grid/offgrid ATS, and it
holds the contactor coils (does not need a new cold-start), I'll probably implement
#152 with option 1 (attended cold start). Grid going down for a period that wouldn't be supported by battery - and I wouldn't be present for - is very unlikely in my case, and the added AT safety is nice to have. People's use cases/risk tolerances may vary and they should implement accordingly.