New Member
- Joined
- Sep 25, 2021
- Messages
- 54
It does NOT hold the contactor coils.. at all. Which gives me faith in the protection circuits, but bums me out because we still have a cold start issue.
I think option 3 of #152 is probably the move here if a fully autonomous system is the goal. This could be executed a couple different ways:
- Blind one-shot (less effort): tie an off-the-shelf timer in parallel to the coil of the N bonding contactor. Program this timer to perform a one-shot ~4-10s hold of the cold start momentary button in #152. This will execute a one-shot, blind cold-start of the system at the same time the neutral bonding contactor is energized (when the ATS goes on->off grid). This is relatively simple to implement and uses off the shelf parts, but has no monitoring, no remote control, and no retry capability.
- Monitored (more effort): use a microcontroller (arduino, esp32, whatever) to handle the cold start process. Big benefit of this is that we'd be able to read voltages, current, and most importantly AT internal temp during bootstrap and running states, and having a connected device with GPIO also opens the door to shipping logs/data, etc.