I have been refining a design for a while and would appreciate suggestion or criticis.
Several directions.
I will have three SPF 5000 ES‘s being fed into an inverter sub panel. This panel will have an Autotransformer attached to it. I was thinking of using the 100A Victron autotransformer. It would we attached to the panels lugs and protection would come thru it breaker. This transformer has a neutral/ground relay that I would energize from the dry contact from the first inverter.
The inverter sub panel has (3) 50A breakers being fed by the inverters and I have a 100A breaker hooked up to my loads sub panel. This breaker has a shut trip coil that I use to shut down the system in case I loose my neutral, it’s cleaner than mounting and wiring a 100A contractor.
Now to an area of concern or question. I am planning 30kw of battery and if all is good I will be able to be 100% off grid. I want to have a smaller genset of 3-4k as a should never need scenario. What I want to do is use a 4th 5000 ES with no grid tie hooked up basically as a battery charger. If battery get below a certain level (TBD) I would auto start the genset, it would then energize the 4th ES which in turn would charge the batteries.By doing this I would not have to worry about ant transfer switching to run the genset. Here where your input is appreciated.
Thanks in advance.
Several directions.
I will have three SPF 5000 ES‘s being fed into an inverter sub panel. This panel will have an Autotransformer attached to it. I was thinking of using the 100A Victron autotransformer. It would we attached to the panels lugs and protection would come thru it breaker. This transformer has a neutral/ground relay that I would energize from the dry contact from the first inverter.
The inverter sub panel has (3) 50A breakers being fed by the inverters and I have a 100A breaker hooked up to my loads sub panel. This breaker has a shut trip coil that I use to shut down the system in case I loose my neutral, it’s cleaner than mounting and wiring a 100A contractor.
Now to an area of concern or question. I am planning 30kw of battery and if all is good I will be able to be 100% off grid. I want to have a smaller genset of 3-4k as a should never need scenario. What I want to do is use a 4th 5000 ES with no grid tie hooked up basically as a battery charger. If battery get below a certain level (TBD) I would auto start the genset, it would then energize the 4th ES which in turn would charge the batteries.By doing this I would not have to worry about ant transfer switching to run the genset. Here where your input is appreciated.
Thanks in advance.