Service Voltage in PH is very localized indeed. Some parts it is 240V, while others its 220V
In Manila it is split phase L1,L2,N. In other parts it is L-N, while others it is L1-L2.
Keep this in mind. You do not want to wire up the GRID's L to Deye's PE terminal.
An OffGrid setup then. You will need hefty battery bank. From late afternoon to early morning (4PM to 8AM), you do not have enough SUN to harvest. You will need to have battery capable of supplying you for this duration, OR be conservative/mindful with your power consumption. Taking hot shower (consumes ~2KW) greatly tax your battery bank. I highly suggests that you replace
all non-inverter appliances such as AirConditioners, Washing Machine, Refrigerators. By doing so, you greatly reduce your battery requirement: 10KWH battery packs costs ~P200K in Philippines. This translates to ~P20 per 1WH. If you can reduce load by 1KW, you can save P20,000 in battery costs; and since this is offgrid setup, you should x14 (at least) to cover 4PM to 8AM. THIS (battery) saving should be enough to entice you to replace your power hungry appliances.
I have a 560AH battery bank and my 750W night load consumes about 10% every 4 hours. If I were to use power hungry AC, I will deplete my battery 20% every 4 hours.
Likewise, A 1HP motor consumes as much as 2000W during start up. You should keep in mind that Deye 8KW will not truly power up 8000 watts of load especially inductive motor loads. You will need to keep a healthy margin to prevent croaking. Watch
You will need an ATS to automatically switch from one power source to another.
How often is power outage in your area? Is this multiple occurances a day?
Do keep in mind, ATS are rated for a few thousand strikes only. Putting your house on the "LOAD" Terminal eliminates ATS need.
Finally, you will also want to charge your batteries from GRID when your battery gets depleted at night. THIS can reduce your battery bank size. You can achieve this using Time of Use system (other inverters do not have this). Something like this:
View attachment 106455
If your battery falls below 50% capacity from 1AM to 5AM, Deye will Grid Charge them to 50%. No need to grid charge to 100% as it will be morning soon and you only want enough power until Sun goes up.
The exact time, battery capacity will greatly depend on your experience - you will be tweaking this as you go along for a period of time.
You made the right choice getting DEYE. It will serve your requirement nicely!
PS. A few days ago, it was rainy and cloudy it barely charged up my batteries. I managed to harvest about 2kwh a day for 2 days. Keep this in mind. You will want more Solar Panels and Grid Charging on specific time to get you through.