I have a Sol-Ark which is essentially a Deye, but with some different screens. On a Sol-Ark there is a Time of Use Setup that brings up days of the week that you want TOU to function. The days also have to be selected.
Here are my setting that works as you wanted.Anyway, trying this now. Switched from voltage to percentage monitoring of the battery. Lowest I could set to in TOU was 20% but I am way above 20%. Turned on grid. Didn't work. JK-BMS shows load to battery went from -9A to about 0, which means the system stopped drawing down the battery, as far as I know. As soon as I turned off the grid again, the JK-BMS again shows the -9A load.
Any other suggestions to try?
YesDo you also have the "Days of the week" settings page shown by @Oldphile ?
Do you have a generator?Here are my setting that works as you wanted.
Yes I have a generator.Do you have a generator?
Is yours an 8K model?
Matching your settings now.
How does OP get to the Days of the Weeks setting?
I tried just paging down on the system settings after the TOU settings page. Is it somewhere else?How does OP get to the Days of the Weeks setting?
2 and 4 I didn't had before it came up after a firmware updateDuplicated your settings, still having the same problem.
Here are differences between my system and yours:
1. I duplicated your generator but I don't have a generator. Maybe I need to uncheck the "gen charge" and "gen sig" checkboxes and not use "Smartload output" option and also remove the "gen" checkboxes in the TOU.
2. I don't have the days of the week setting.
3. Battery capacity I listed 280ah, you have 1108ah
4. I don't have "off grid immediately off" checkbox on the generator menu.
Otherwise everything else is the same.
I don't know how to check this. The checkbox at the top is checked if that is your question.You check your tou settings are activated?
YesI don't know how to check this. The checkbox at the top is checked if that is your question.
Do you have a diagram how you have all connected and CT's position?
Me think so when you switch on grid.I also don't have a CT connected. Is that relevant?
Not sure but if its not to much trouble give it a shot because I'm out of ideas.Ok I found the box with what must be the CT. Checking the manual as to what to do with it. This isn't the source of my problem is it?
Was your Time of Use settings working before your firmware update?2 and 4 I didn't had before it came up after a firmware update
Just to be safe shut down.Ok trying the 2 CT. I see how they should be connected.
Can I connect the CT to the pins with the inverter on? Or should I shutdown before connecting the leads?